Just to make clear, incase anyone reading this didn't know, a Martindale socket tester will not pick up a neutral/earth crossed connection which is why the correct dead tests are so important.
Discuss Neutral earth fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Just to make clear, incase anyone reading this didn't know, a Martindale socket tester will not pick up a neutral/earth crossed connection which is why the correct dead tests are so important.
I always carry out the sequence of tests in the order I was taught at college, I do a Ze test before starting the design for a new installation, all the rest of my live testing is done after all the dead testing has been done. I only do new installations though so that is why I don't rely on Zs testing, I just use calculation.
You don't record r1 + rn, but you do do it. Look in on site guide, how to test a ring. Tells you step by step.
If you have got red on site guide, bottom of page 81. Continuity of ring final circuits, step 2.
There is also, on pg 38 of GN3, an explanation of (r1+rn)/4
Absolutely. All that said, a thorough R1R2 will pick up cpc in the wrong terminal anyway.
Exactly! Isn't this the point? Even if an R1+Rn wasn't done (which it should be, according to the guidelines) a R1+R2 would still pick up this fault.
And two modular sockets are two separate sockets so both need to be tested. An easy to mistake to make but an error in the testing all the same.......
Yes, I'd agree with that.Nice one Spin
So are we agreed, that an R1R2, would have picked up the fault, and despite what some books say, R1Rn was not needed? (going away a little from the OP).