Favour for a mate has turned into a nightmare. Really appreciate any comments on the below!

Was asked to look at some sockets which have apparently been "sparking".......

17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!

Ze 0.32. TNS

Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.

Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)

So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!

After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.

It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?

Am i missing anything here? neutral to earth faults always mess with my head.

Any advice will be helpful. Constructive or otherwise!!
 
Favour for a mate has turned into a nightmare. Really appreciate any comments on the below!

Was asked to look at some sockets which have apparently been "sparking".......

17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!

Ze 0.32. TNS

Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.

Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)

So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!

After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.

It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?

Am i missing anything here? neutral to earth faults always mess with my head.

Any advice will be helpful. Constructive or otherwise!!
Bit of IR testing would be my choice for starters.
 
Probably lost the earth somewhere
 
  • Like
Reactions: pc1966
That makes sense why the rcd not tripping.

Little confused about my ir readings though

Is that figure of 8 Ohms supposed to be 8 Megohms?
 
Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)
Can you use a wander lead and check for connectivity of both N & E back to the CU?

As already said above, it looks like an open E as if it were N-E short you probably would see the RCD trip.

N-E faults though are tricky as if you have a very low supply side N-E voltage, say TN-C-S, then you may only get enough residual current flowing when there is a big load on some branch giving enough volt drop on the neutral conductor to cause 30mA of stray current to trip the RCD at the location of the fault.
 
Your observations are in conflict. If there is a dead short between N & E, there can't also be 30V between them. Or is the 30V at the sockets that don't have the short? It could be that the CPC is severed and one side of it is down to the neutral. Someone came along and discovered the break, turned the circuit into two radials without disconnecting the faulty leg, and the N-E breakdown has since developed.
 
  • Like
  • Winner
Reactions: Pete999 and DPG
Can you use a wander lead and check for connectivity of both N & E back to the CU?

As already said above, it looks like an open E as if it were N-E short you probably would see the RCD trip.

N-E faults though are tricky as if you have a very low supply side N-E voltage, say TN-C-S, then you may only get enough residual current flowing when there is a big load on some branch giving enough volt drop on the neutral conductor to cause 30mA of stray current to trip the RCD at the location of the fault.
I will be wandering leading as you suggested on my next visit. Thank for your response, very helpful.

Your observations are in conflict. If there is a dead short between N & E, there can't also be 30V between them. Or is the 30V at the sockets that don't have the short? It could be that the CPC is severed and one side of it is down to the neutral. Someone came along and discovered the break, turned the circuit into two radials without disconnecting the faulty leg, and the N-E breakdown has since developed.
Yes i am thinking i am at fault.

I didn't think to end to end at the time, only really made the connection as possible ring when closing up the CU. but having a faulty leg which has deteriorated further makes sense.

appreciate the help.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
St Albans

Thread Information

Title
Neutral to earth voltage
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
New guy 397,
Last reply from
New guy 397,
Replies
8
Views
5,428

Advert