Favour for a mate has turned into a nightmare. Really appreciate any comments on the below!

Was asked to look at some sockets which have apparently been "sparking".......

17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!

Ze 0.32. TNS

Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.

Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)

So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!

After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.

It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?

Am i missing anything here? neutral to earth faults always mess with my head.

Any advice will be helpful. Constructive or otherwise!!
 
Favour for a mate has turned into a nightmare. Really appreciate any comments on the below!

Was asked to look at some sockets which have apparently been "sparking".......

17th edition board. 100amp/30ma RCD as main switch and only additional protection for 11 circuits. Unsure if that conforms with BS EN 60947-3?!

Ze 0.32. TNS

Bonding appears good, only ohm tested across exposed metal work couldn't find actual straps, but it leaves from the CU.

Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)

So i'm assuming we have a poor neutral joint somewhere between the good and bad sockets...why is the RCD not tripping when load is applied to these sockets?!

After taking the entire circuit apart i couldn't find the smoking gun, so now i'm working on the assumption a joint in the ceiling.... At which point I threw in the towel isolated the circuit and said i'd have to come back ASAP.

It also looks likely that that 2x B16 radials use to be a ring (flagging on cables with tape in CU). Would that change anything?

Am i missing anything here? neutral to earth faults always mess with my head.

Any advice will be helpful. Constructive or otherwise!!
Bit of IR testing would be my choice for starters.
 
Unable to perform a Zs at 4 sockets from 8, Error 4 on my fluke. >50v N->Earth. Rest of circuit tests no issue. 2.5mm radial.

L->E 240v
L->N 240v
N->E 30v(ish)
Can you use a wander lead and check for connectivity of both N & E back to the CU?

As already said above, it looks like an open E as if it were N-E short you probably would see the RCD trip.

N-E faults though are tricky as if you have a very low supply side N-E voltage, say TN-C-S, then you may only get enough residual current flowing when there is a big load on some branch giving enough volt drop on the neutral conductor to cause 30mA of stray current to trip the RCD at the location of the fault.
 
Your observations are in conflict. If there is a dead short between N & E, there can't also be 30V between them. Or is the 30V at the sockets that don't have the short? It could be that the CPC is severed and one side of it is down to the neutral. Someone came along and discovered the break, turned the circuit into two radials without disconnecting the faulty leg, and the N-E breakdown has since developed.
 
Can you use a wander lead and check for connectivity of both N & E back to the CU?

As already said above, it looks like an open E as if it were N-E short you probably would see the RCD trip.

N-E faults though are tricky as if you have a very low supply side N-E voltage, say TN-C-S, then you may only get enough residual current flowing when there is a big load on some branch giving enough volt drop on the neutral conductor to cause 30mA of stray current to trip the RCD at the location of the fault.
I will be wandering leading as you suggested on my next visit. Thank for your response, very helpful.

Your observations are in conflict. If there is a dead short between N & E, there can't also be 30V between them. Or is the 30V at the sockets that don't have the short? It could be that the CPC is severed and one side of it is down to the neutral. Someone came along and discovered the break, turned the circuit into two radials without disconnecting the faulty leg, and the N-E breakdown has since developed.
Yes i am thinking i am at fault.

I didn't think to end to end at the time, only really made the connection as possible ring when closing up the CU. but having a faulty leg which has deteriorated further makes sense.

appreciate the help.
 

Reply to Neutral to earth voltage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
628
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
270
Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
M
Hi Guys I purchased some of the above online around 3 weeks ago, They are a fairly new product, very usefull as you can change both colour from...
Replies
1
Views
308
2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock