- Reaction score
- 1
So looking at a system that utilises a couple of sizable UPS unit to supply various equipment through a site. The UPS is static with 3 phase output, both units have an input switchboard and output switchboard with a castell interlock so that the bypass can not be switched in unless the UPs itself is in bypass.
I had a look around at the original drawings and noted that this UPS sometimes operates with the neutral earth link out of circuit. when switching between mains and generator there is a time that the system is operating without the neutral earthed. The feeder to the UPS input board circuit breaker turns off on a power outage until the power is restored, either from a generator or from one of the other buildings on site.
I thinki it needs to be looked at and some form of isolation transformer fitted so that there can be a permanent neutral earth link on the supply to the UPS rather than what is there. the other site electrician is recommending fitting in earth relays but that well i dont think would be that great a solution, to have to depnd on another system to maintain the neutral grounding.
I had a look around at the original drawings and noted that this UPS sometimes operates with the neutral earth link out of circuit. when switching between mains and generator there is a time that the system is operating without the neutral earthed. The feeder to the UPS input board circuit breaker turns off on a power outage until the power is restored, either from a generator or from one of the other buildings on site.
I thinki it needs to be looked at and some form of isolation transformer fitted so that there can be a permanent neutral earth link on the supply to the UPS rather than what is there. the other site electrician is recommending fitting in earth relays but that well i dont think would be that great a solution, to have to depnd on another system to maintain the neutral grounding.