Hi all,

Pricing for a supply to a 25x 10M steel frame shed around 100M from a bungalow, one section is going to be partitioned to create a stable area.

Is there any requirement for a 300ma S type RCD?, I wouldn’t really class it as agriculture. Only 2 double sockets well away from the stable area In the tack room.

Thanks
 
Just Been out for a look, supply is TNCS. I shall TT the outbuilding with 100mA s type at the mains position. Bonding the metalwork and an additional earth spike. 16mm 2 core to the shed. All final circuits will have 30mA RCD protection
 
Just Been out for a look, supply is TNCS. I shall TT the outbuilding with 100mA s type at the mains position. Bonding the metalwork and an additional earth spike. 16mm 2 core to the shed. All final circuits will have 30mA RCD protection

Why the 100mA RCD at the mains position? The submain will be connected to the Tncs earthing system so won't need it.
 
Just Been out for a look, supply is TNCS. I shall TT the outbuilding with 100mA s type at the mains position. Bonding the metalwork and an additional earth spike. 16mm 2 core to the shed. All final circuits will have 30mA RCD protection
Why the 100mA RCD at the mains position? The submain will be connected to the Tncs earthing system so won't need it.
Far better to do what Dave has suggested, if you use a 100ma S type at source and use RCBO's for the final circuits you will have to use DP RCBO's. This is because standard RCBO's are SP and when tripped will not disconnect a N-E fault possibly resulting in the 100ma device tripping as well. This is commonly overlooked on TT systems.
 
So earth the armour from using the TNCS earth and isolate from then TT earth and Carey on as Normal
 

Reply to Outdoor building/stable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

You brainy guys may be able to help with this thought I was having. There has been a thread recently about 4mm radial from ring main. This got me...
Replies
29
Views
3K
All. Bear with me. I'm doing some research into electrical installation into timber framed buildings. This is not about a new build in first fix...
Replies
10
Views
1K
Hi all, I have never had to look into a job like this before but I have had an enquiry from a customer who is having a supply brought from the...
Replies
22
Views
7K
Hi there. I'm building a house and need some help with the LED lighting design. Lots of experience wiring things, some experience using LEDs (did...
Replies
8
Views
2K
Hi all, I'm in need of a bit of clarity on this decision. So, long story short... have been asked to quote for the installation of some...
Replies
27
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock