So yes the pipe to the toilet cistern is copper and extraneous, it is bonded with a strap and earth cable running back to the CU main earth block.
Good stuff, though are you 100% sure that is where it goes? (The fact there is bonding in this location at all suggests someone has already considered this topic and it is supplementary bonding that links up to other accessories in the room.)
The idea is that you can't touch a faulting accessory (e.g. shaver socket) and path to earth without both things being held at the same potential via a direct link of low resistance.
With the resistance test, if they were to check the taps, they would be open circuit due to the plastic pipes, how would they know the difference between a failed bonding test and plastic pipe?
Well to be extraneous it has to leave the room, so first you try and test to somewhere handy just outside e.g an airing cupboard or sometimes a combi boiler. If it's testing open circuit it's reasonable to assume they are plastic pipes or there's an insulated joint in the middle.
If it's low-ish, then you test from the tap to a cpc in the room, and you then find out whether you are looking at the resistance of a fairly short length of bonding cable, OR a larger resistance representing the total path along the pipe, via the main bonding, to the MET, back to the consumer unit and along the CPC of the circuit.
You need an accurate continuity tester (or multi function tester) to do this, multimeters are usually not accurate enough.
We have gone down a slight rabbit hole here - it's a much better use of effort to get the CU upgraded so the complexities of this topic can be brushed aside!
So now the question is, can I pass a EICR as it stands with the original consumer units and no RCD?
I'm not trying to be pedantic, but EICR's aren't pass or fail, you get a report with C1 (dangerous), C2 (potentially dangerous), C3 (improvement recommended).
If rented out C1's and C2's are supposed to be rectified within a fixed time frame (which I forget tonight - 2 weeks?).
If privately owned, you ignore C2's and above at your own peril!
Yes, it is possible to only have C3's in your situation.
It's still a flipping good idea to have RCD protection though!