Aug 30, 2022
30
Bournemouth
Hi all,
I'm refitting my bathroom in my first floor flat (top floor) built around 1989. It has 2 CUs, one for night storage and one for 24h electrics, they are of the 1980's era Crabtree, the label on the side says BS5486:PART 13 CM16.
The hot and cold are run in plastic from the Immersion heater located outside the bathroom.
The mains water is supplied to the flat in plastic and then copper to the kitchen sink and toilet, this is "bonded" to the CU earth terminal.
Items with potential in the room :
The toilet has a short piece of copper pipe in the Outside Zone to the cistern.
There is a fan isolation switch in the Outside Zone (the fan unit is in the loft).
There is a shaver socket in the Outside Zone (isolation transformer type).
The ceiling is 2.45m high and therefore in the Outside Zone I believe.
I would like to fit fire rated IP65 downlights to the existing lighting circuit (which also has the fan and shaver socket on it).
So in short, there will be nothing with any potential in Zones 0,1 or 2. and there will be no new circuits.
Am I right in thinking that changing a central light to 4 downlights is not classed as a new circuit?.
I know a RCD is desirable but is it strictly necessary in this instance?
The flat will need to pass a EICR but I realy don't need the expense of changing the CUs as I'm on a budget.
Cheers,
John
The alteration will need to comply with current Regulations so bathroom or not 30ma rcd protection is required.
Thanks Westward,
I feared as much, that's why I went into such detail to make sure. I'm not an electrician and don't know the current regs, only what I've gleaned.
What are my options?
RCBO?
Surface mount RCD?
New CU?
Anything else?
If I go with a new CU, does this mean I will need to replace both CU's? Each has its own feed from the meter, the storage heat times are controlled by SSE "teleswitch" and the meter switches on the extra live out when commanded.
Cheers
Is your consumer unit Crabtree Starbreaker.
Reactions: Johnstar
I don’t think so, here are some photos
Looks like an SB6000, is that a Starbreaker
No they are SB6000. They did make rcbos for them but were two module and would now be second hand. Finding one for a 6 or 10A lighting circuit is likely to be difficult. It is likely they never existed.
Thanks.
so the RCBO route is out really.
If I were to just replace the central light with a new modern one, would that also need an RCD?
And a difficult question to answer, but I won’t hold you to it, if nothing changes, is the Flat likely to fail a EICR on the Consumer Units alone I.e. age and lack of ECB, assuming everything else in the flat is ok?
Are you going to be renting this flat out to tennants?
Reactions: Johnstar
Hi DPG,
Not at the moment but I may do in the future.
Do you know if there is supplementary bonding in the bathroom? If there isn't it would be much easier to change the CU than to add it.
Assuming it does have the supplementary bonding, and noting it is a a top floor so no sockets are likely to be used outside, it wouldn't have automatic C2's fail for lack of RCD protection according to BPG4. This assumes the installation tests as fault-free in every other regard.
No one should be entertaining a rental property without RCD protection these days though, it's just common sense that you want tenants to have a level of safety that is now commonplace among dwellings.
Hi DPG,
I'd be very wary of renting it out with no RCD protection anywhere.
Hi Tim, thanks for your answer.
I accept that RCDs should be fitted for rentals and that is something to consider.
Re the sup. bonding. The pipes are all plastic (save the toilet) so there is nothing to bond. There is a bit more detail on that in my first post.
So given the plastic pipes and if the Flat passes all tests, there is no obvious reason why the current CUs should cause a fail assuming they are in good order?
How would a tester go about checking the plastic pipes?
Yes, understood. I have been told I need an EICR by the management company. I’m starting to think that they have this wrong as I’m the owner and it’s not going to be rented in the near future anyway.
As it’s just me, I’m happy without any RCDs especially due to the cost ( I’m guessing hundreds of £s) but I’m worried that when I get it inspected it will fail. Now I’m questioning if I need to get it inspected at all?
Another thought.
In a building such as yours, each flat is its own fire compartment. This means that surfaces like ceilings are specified and installed as fire barriers.
Turning a fire barrier into something resembling swiss cheese to fit a few downlights need special consideration.
You must, must fit fire-rated downlights so that, should a fire start in your fire-compartment, that it cannot spread quickly, through your downlight holes and into the roof of the building.
Another thought.
A good thought, the downlights I was thinking of are 60 minutes rated (which exceeds that of the current single layer of 12mm plasterboard) IP65 rated and Insulation Contact rated. The loft space is compartmentalised from the other flats. It is a 2 story building with 6 flats.
A single layer of standard Gypsum plasterboard has no specific fire-resistance.
Your ceiling is probably one of the Fireline products - these are 15mm and covered with pink, not brown paper.
Reactions: Johnstar
I hope you’re right. It looks like standard board though and I’ve been around a lot of plaster board. Anyway, I probably won’t fit downlights now. Can’t afford for it to fail the EICR tests at the moment.
Hi again Tim, when I get it tested, how does the tester assess the supplementary bonding? If it is by inspection should I remove the bath panel so that they can see the pipes?
So I have now read that a domestic dwelling should have a EICR every 10 years and if rented every 5 years
No, I wouldn't remove the panel (oh that all home owners would think in such an obliging way!)
A lot of installations would meet the 3 requirements in section 701 (automatic disconnection of supply for all circuits in room, RCD protection for all circuits in room, and all extraneous conductive parts are bonded) which would mean supplementary bonding isn't required.
You don't have RCD protection for all circuits in room, so be default supplementary bonding is required.
So next question is are there any metallic parts that could introduce a potential in the bathroom (extraneous conductive parts).
If there are then the CPC of all circuits in the room need to be connected to the extraneous conductive parts with supplementary bonding.
From what you've said it sounds as though the copper pipe to the toilet cistern might be a contender.
You haven't mentioned any heating in there - is the a radiator / towel rail with metal pipes?
Having determined that supp. bonding is required, and there are items that require it, it's usually quickest to use continuity tests to check the resistance between the items is low enough to keep the touch voltage below 50v. There's a formula in the regs for how low it needs to be.
Reactions: Johnstar
Lovely reply Tim,
So yes the pipe to the toilet cistern is copper and extraneous, it is bonded with a strap and earth cable running back to the CU main earth block. The other parts that introduce potential are the fan isolation switch and the shaver socket both with metal back boxes connected to the protective conductor. The one central light also has a metal case and I will replace this with a modern plastic one. All of these are in the Outside Zone. The light switch is outside the room.
There is no heating in the room and no other metal parts entering from outside.
With the resistance test, if they were to check the taps, they would be open circuit due to the plastic pipes, how would they know the difference between a failed bonding test and plastic pipe?
Yes. Domestic installs now all circuits require RCD protection if i remember rightly. Would have to check regs to be 100% but as far as i remember you're only allowed to not have RCD protection in commercial premises and only when the appropriate risk assessments have been done to justify not having it.
Hi,
Thanks this was also pointed out by Westwood so I have decided to leave the electrics alone and just change the light fitting to a modern one. I did fancy downlights but it’s going to be too expensive if I have to fit an RCD.
So now the question is, can I pass a EICR as it stands with the original consumer units and no RCD?
Good stuff, though are you 100% sure that is where it goes? (The fact there is bonding in this location at all suggests someone has already considered this topic and it is supplementary bonding that links up to other accessories in the room.)
The idea is that you can't touch a faulting accessory (e.g. shaver socket) and path to earth without both things being held at the same potential via a direct link of low resistance.
Well to be extraneous it has to leave the room, so first you try and test to somewhere handy just outside e.g an airing cupboard or sometimes a combi boiler. If it's testing open circuit it's reasonable to assume they are plastic pipes or there's an insulated joint in the middle.
If it's low-ish, then you test from the tap to a cpc in the room, and you then find out whether you are looking at the resistance of a fairly short length of bonding cable, OR a larger resistance representing the total path along the pipe, via the main bonding, to the MET, back to the consumer unit and along the CPC of the circuit.
You need an accurate continuity tester (or multi function tester) to do this, multimeters are usually not accurate enough.
We have gone down a slight rabbit hole here - it's a much better use of effort to get the CU upgraded so the complexities of this topic can be brushed aside!
I'm not trying to be pedantic, but EICR's aren't pass or fail, you get a report with C1 (dangerous), C2 (potentially dangerous), C3 (improvement recommended).
If rented out C1's and C2's are supposed to be rectified within a fixed time frame (which I forget tonight - 2 weeks?).
If privately owned, you ignore C2's and above at your own peril!
Yes, it is possible to only have C3's in your situation.
It's still a flipping good idea to have RCD protection though!
Reactions: Johnstar and DPG
This is not correct.
Thanks once again for a great reply.
First point is yes, I’m absolutely sure because I stripped out (cut off) the old copper pipes as they were 15 mm copper sunk into the concrete floor with no insulation or protection of any kind. As I was replacing the old fortic cylinder with a mains pressure one I didn’t trust the old pipes. I’ve run the new pipes from the new cylinder in plastic up and through the loft. Plastic for lower heat loss and ease of run. The old pipes were bonded and connected to the earth block via a thick cable that runs up to the loft and down to the earth block next the CUs.
It’s very difficult to see how you could get a shock in this room as there is simply very little in there and very little exposed at earth potential, the very short pipe to the cistern, and the 4 screw heads for the fan switch and shaver socket.
I agree completely that an RCD would be best and safer but changing the two consumer units is an expense I can’t afford at the moment with everything else going on. Should I rent it in the future I will however change the CUs.
Thanks for the information about the EICR and testing I didn’t know that about the fault classifications.
I remember using a Mega when testing for earth continuity on industrial equipment, it used a much higher current than a standard multimeter and could measure very low resistances. I guess there is an equivalent that you guys use for this work.
Thank you very much Tim this has made things much clearer for me.
Cheers
Reactions: Jim_e_Jib and DPG
Utter nonsense!
I remember looking for a 6A one a few years back. I found a few 32A and 16A but never any other rated ones.
That's not surprising, in those days the use of RCBO's was much like the current situation with AFDDs. Most people didn't see the need for them, some people did fit them but only when absolutely necessary and that would almost exclusively be socket circuits hence 32A being the most commonly available 2nd hand.
Reactions: DPG and Johnstar
Lol you've glossed over where i said i wasn't sure?
You know it would add to the conversation if you actually said what the rule was instead of just saying 'nonsense'.
Just for giggles mate, you said that you weren’t 100% sure which mean that you were somewhere between 0% and 99% sure. It would be useful if you could narrow down the range of sureness a bit! 😂 😂
No offence mate just giggling 🤭
Hi,
Found this in a video of 18th addiction changes.
It’s not the full regulation, just an overview of what has changed since 17th but it does mention the risk assessment.
The vid is by John Ward
Hi,
JW makes good videos, but due to the whirlwind world we live in it is sadly already out of date as amendment 2 to the 18th edition (mandatory from end of current month) has further changes.
From a domestic point of view you mainly need to know that the latest regs require socket circuits and lighting circuits to have 30ma Type A RCD protection. New work needs to meet this standard.
While a risk assessment and omitting RCD protection is possible, the permitted circumstances are so narrow in amendment 2 that it isn't worth describing it in detail. It will never apply to domestic installations as there will always be unskilled / ordinary people present.
Reactions: Johnstar
To summarise my situation:
If I change the existing light for another it is NOT a new installation.
If I replace the light with say 4 downlights then it IS a new instillation.
All new instillations have to meet the current regs which means an RCD would be mandatory.
There is no requirement to fit an RCD as long as the unchanged current installation complies with the regulations at the time it was designed (1989) with bonding.
It is always desirable and safer to fit an RCD and I will do this when I have the money and at that point I may fit the downlights.
Why engage the keyboard if you are not sure if your wrong you are most certainly going to be shot down
Reactions: loz2754
It is quite common for management companies who are managing blocks of flats to require an EICR every 5 years for all the individual flats regardless of whether they are owner occupied or rented out to ensure all parts of the property is a safe condition
The problem you may have is the condition of the electrical installations in the other flats if they all have RCD's it may look odd that you haven't and the management company may request that you fit them. The part of the EICR that may draw attention to the lack of RCD's is the observations as codings will highlight the parts of the installation that needs improvement or remedial work
Hi UNG,
Thanks for the reply, a bit more for me to consider.
On a further note, I have two CUs in the flat one that is energised twice a day for storage heat and hot water and the other for lights and sockets etc.
Given the storage heat one does not have any sockets attached as the heaters all have switched fixed outlets, does that also come under the RCD regulations?
I keep reading RCDs are required for lights and sockets, no one mentions fixed outlets.
Any cable buried in a wall at a depth of between 0 mm and 50mm needs 30mA max. RCD protection .
Thanks Brian,
That makes sense, just in case someone bangs a nail in ⚡
Bournemouth
Bathroom refit, do I need a RCD?
Johnstar,
Johnstar,