Discuss r1+r2. calculate or measure... in the UK Electrical Forum area at ElectriciansForums.net

Obviously it has to be measured when testing, otherwise how can you be certain your circuit will disconnect as it should under fault conditions ?
 
(r1 + r2)/4=R1+R2
So you know what you get when you cross them over at each socket.
I hear some miss doing the cross overs and just check the with a socket tester.

Have I gone off on a tangent again!
 
Apologies abit (very) vague . Upon undertaking a conditon report and the circuits have been energised for many years. Do you measure r1+r2 or just do Zs/Ze and calculate r1+r2. For socket circuits odviously the correct test procedure needs to be done.

For example R1+R2 on a lighting circuit in small flat is say 2.50ohms you'd immediately know loose connection. Yet you could take a Zs on the same circuit and it could be more like 0.70ohms. (something to do with the current from the test kit i believe, but i dont know correct terminology) I think its more important to do r1+r2 because of this. Also parallel paths occasionally bringing Zs values down.

Please discuss :)
 
You measure R1+R2 as this also show continuity R1+R2=Zs-Ze
Measure.Zs were possible Zs=Ze+R1+R2
Ze by asking or measuring Ze=Zs-R1-R2

Also note that r1, r2, and rn are ring values
 
So they do. My point is simple enough isnt it??

No your point isn't simple enough, I haven't got a clue what you are talking about here.

You say some people just do a Zs test, and as I pointed out some people do no tests at all. Neither of these makes them correct just because some people do it.
 
Apologies abit (very) vague . Upon undertaking a conditon report and the circuits have been energised for many years. Do you measure r1+r2 or just do Zs/Ze and calculate r1+r2. For socket circuits odviously the correct test procedure needs to be done.

For example R1+R2 on a lighting circuit in small flat is say 2.50ohms you'd immediately know loose connection. Yet you could take a Zs on the same circuit and it could be more like 0.70ohms. (something to do with the current from the test kit i believe, but i dont know correct terminology) I think its more important to do r1+r2 because of this. Also parallel paths occasionally bringing Zs values down.

Please discuss :)

Now thats more like it :)

I see what you are getting at now. The original question looked like 'do you measure or calculate?'... well I suppose that was the original question, which has an obvious answer as DS explained.

I think you are now asking (and possibly meant this is the OP) would you just do a Zs rather than measure R1+R2 and add it to Ze?

If it was a condition report as you state then I would do both. I would measure R1+R2 and measure Zs because that is what the form requires. If it was a small job that I was undertaking and it was a MWC being issued then I would just measure the Zs.

As said before the only time I would 'calculate' (ie look up the figures for R1+R2) rather than 'measure' R1+R2 would be when deisigning a circuit.
 
Last edited:
No your point isn't simple enough, I haven't got a clue what you are talking about here.

You say some people just do a Zs test, and as I pointed out some people do no tests at all. Neither of these makes them correct just because some people do it.

I prefer to measure R1+R2 Ze and mostly calculate Zs. For the reasons i have explained above. Im after others opinions. Now im simply after a discussion on what others prefer / do and why. It really is simple buddy. It really is.
 
I prefer to measure R1+R2 Ze and mostly calculate Zs. For the reasons i have explained above. Im after others opinions. Now im simply after a discussion on what others prefer / do and why. It really is simple buddy. It really is.

Yes it is really simple, you test the continuity of the CPC and you test the EFLI.

You test the continuity of the CPC either using the R1+R2 or R2 tests. On a condition report you generally test R2 rather than R1+R2 for reasons of practicality.
You test EFLI on the live circuit to ensure fault protection will operate within the required time etc.

DON'T CALL ME BUDDY!
 
Sorry boys- Stop this abrasive attitude it can only send this thread downhill, if you cannot be civil with each other stop replying and move on.

If you want to carry on then the thread will be closed and as we do not condone this type of abrasive attitude and we will implement a ban - if you feel any member is out of order then use the report button please don't take it on yourself to exacerbate the situation.
 
Last edited:
It is permissable to calculate Zs from measured values. It is always preferable to measure Zs though.
It is not permissable to calculate R1+R2 from other measured values. It must be measured.

The main purpose of EICR testing is to ascertain compliance for disconnection times and safety for continued use of circuits.
To this end some £80 a time jockeys don't do continuity testing.
I always perform a full range of tests on all circuits.

I think this is what you were asking about.
 

Reply to r1+r2. calculate or measure... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi forum, A question about R1+R2 testing. I’m testing a lighting circuit. It’s an old circuit with old colours. In the control panel feeding the...
Replies
7
Views
3K
hi all just got a Q regarding how to find R1 then second Q how to find R2 what i did so far was mutiplying each answer for1.67 so I could get the...
Replies
11
Views
842
Have only recently gotten in to testing. Doing an R1+R2 on a lighting circuit but instead of producing a result my tester clicks over and over...
Replies
5
Views
899
When we measure R1 + R2, we're essentially saying R1 is resistance of the line, and R2 is resistance of the CPC, and we add them together. But...
Replies
13
Views
2K
So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock