hello every one i have a problem. i have been called out to a commercial kitchen where the 16A b type RCBO keeps tripping when you turn off a 20A DP switch that controls two dimmers which in turn supplies 2 sets of heat lamps
300w x 5 halogen lamps and 250w x 5 inferred ES lamps.
when the inferred lamps are turned off it trips the RCBO but only.

the inferred at present are not on the dimmer as dimmer is not working

I have tried having only the inferred on but trips cable bells out fine so now scratching my head
 
Change the switch one pole maybe breaking before the other, a significant break causing an imbalance.
 
  • Agree
  • Like
Reactions: static zap and ipf
hello every one i have a problem. i have been called out to a commercial kitchen where the 16A b type RCBO keeps tripping when you turn off a 20A DP switch that controls two dimmers which in turn supplies 2 sets of heat lamps
300w x 5 halogen lamps and 250w x 5 inferred ES lamps.
when the inferred lamps are turned off it trips the RCBO but only.

the inferred at present are not on the dimmer as dimmer is not working

I have tried having only the inferred on but trips cable bells out fine so now scratching my head
What are you inferring?
Sounds like it might be a problem with the switch controlling the infrared fittings.
 
Can't get away with a thing on here. ;)
 
  • Funny
Reactions: Wilko
Have you done any testing of the circuit? (what's belling out?) The first thing I would do is verify insulation resistance is sound before looking at other causes.
[automerge]1584727827[/automerge]
Change the switch one pole maybe breaking before the other, a significant break causing an imbalance.
In theory one pole breaking before the other should not cause an imbalance. An imbalance in the line and neutral current should only be the result of leakage, usually to earth. Two poles breaking at different times will not result in different line and neutral currents.
 
Last edited by a moderator:
It's an RCBO, can't be sure why it's tripping. Is it necessarily leakage?
Correct testing (and inspection) is required.
 
Have you done any testing of the circuit? (what's belling out?) The first thing I would do is verify insulation resistance is sound before looking at other causes.
[automerge]1584727827[/automerge]

In theory one pole breaking before the other should not cause an imbalance. An imbalance in the line and neutral current should only be the result of leakage, usually to earth. Two poles breaking at different times will not result in different line and neutral currents.
This has occurred several times on here especially with cooker isolators, replace it problem solved.
 
  • Informative
Reactions: radiohead

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
north east england

Thread Information

Title
RCBO tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
albi,
Last reply from
albi,
Replies
7
Views
2,882

Advert