Strictly speaking you must meed the disconnection times on all final circuits, how you achieve that is open.

But given the high Zs for TT systems the only practical solution is going to be RCD protection for all circuits. So you do not have to have an RCD incomer if every final circuit has RCD protection.

Having said that, if you have a fault to earth your only means of disconnection is the RCD, so it had better work! That is one reason I would always prefer on TT to have the likes of a 100mA S-type up-front and 30mA RCBOs for the final circuits providing per-circuit additional protection. If one RCBO fails to trip the incomer still should open. But that is going to cost a lot more than some folk can afford, and is not strictly necessary as a single working RCD is sufficient.
 
The main switch does not have to be an RCD. However the incoming tails must be suitably support and protected so that under fault conditions the cahssis of the board will not become live and present danger.

i.e. Use of suitable cable entry gland, cable grip etc.
 
As above cable glands!

Everyone should be using cable glands for tails & earth, not just for protection against the edge of the hole, but to provide strain relief as well. Also maybe the Doncaster 19-strand easy fit tails, makes life easier for you fitting it, and less strain passed on to the terminals to risk any wires coming out.

Cable glands, did I mention them?
 

Reply to RCD Main switch on TT system in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
863
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Special location a Static caravan TT System, CU fitted Main Switch then RCBO’s any comments
Replies
3
Views
766
Hi do tt earth systems highly require a rcd, and if not are upfront rcds a must in the tt earthing systems? Cheers
Replies
27
Views
3K
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
297

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock