Hello all. Can anyone inform me on what the latest guidance on the frequency of RCD testing is? I test my RCD's annually and record the x1/2, x1 and x5 trip and 0-180degrees annually, and replace failures. I also carry out a functional test whilst I'm doing this, and then a further functional test 6 months later. The Distribution boards were installed in 2013 (17th edition) Is this frequency of testing sufficient?
 
Hello all. Can anyone inform me on what the latest guidance on the frequency of RCD testing is? I test my RCD's annually and record the x1/2, x1 and x5 trip and 0-180degrees annually, and replace failures. I also carry out a functional test whilst I'm doing this, and then a further functional test 6 months later. The Distribution boards were installed in 2013 (17th edition) Is this frequency of testing sufficient?
Functionally every 6 months.

There is no longer a requirement to perform a test using a test current equal to or higher than five times the rated residual current.
 
Last edited:
In 2017 the boards should have been labelled with an RCD Test Notice indicating a quarterly test interval for the functional test. Recent 18th edition has increased this functional test to 6 monthly or bi-annually test intervals.
For certification, the instrument based test is now a single 1x test for 18th but other tests may be carried out too(for installers benefit). This should be tested at installation, any subsequent work on the circuit/installation thereafter and then at the recommended interval for a periodic inspection (ie 5 or 10 years etc).
Failure of the functional test should require further investigation by a qualified electrician who may then carry out further tests .5x, 1x, 5x, Ramp etc to evaluate the RCD.
 
  • Like
Reactions: PS Electrics
The functional test interval was actually decreased not increased.
 
The functional test interval was actually decreased not increased.
To be pedantic, if you go from 3 months interval to 6 months you are decreasing the frequency of testing and increasing the length of the interval between tests?? :mask:
 
A 3months interval to 6months interval is a 'decrease'?
£100 per 3 months changing to £100 per 6 months is a decrease.
 
A 3months interval to 6months interval is a 'decrease'?
What I meant to say obviously badly was the amount of times a functional test should be carried out in 12 months is less so a decrease.
 
  • Like
Reactions: DPG
What I meant to say obviously badly was the amount of times a functional test should be carried out in 12 months is less so a decrease

I think everyone knew that but couldn't resist a ribbing 😂
 
A 3months interval to 6months interval is a 'decrease'?
If you look at it as the number of tests required in a year. An RCD test every 3 months is 4. An RCD test every 6 months is 2.
So, a decrease in occurrence of the test.
 
Cant believe its caused so much debate and always more than one way of looking at things!

In 'Extending' the test interval from 3 to 6 months is an 'increase'
quarterly test interval for the functional test. Recent 18th edition has increased this functional test to 6 monthly or bi-annually test intervals.

in the 'test interval' which is what I was referring to in my post#3.

Its obvious that longer intervals will result in fewer tests
 
Cant believe its caused so much debate and always more than one way of looking at things!

In 'Extending' the test interval from 3 to 6 months is an 'increase'


in the 'test interval' which is what I was referring to in my post#3.

Its obvious that longer intervals will result in fewer tests
The time interval between tests has increased. the regularity has decreased. Einstein understood these things.
 
  • Like
Reactions: nicebutdim and DPG
Bi annual is that twice a year or once every two years lol
 
Biannual” means occurring twice in one year, and “biennial” means happening once every two years;)
 
  • Like
Reactions: newfutile

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
London

Thread Information

Title
RCD testing
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
MarkyofftheMark,
Last reply from
mainline,
Replies
14
Views
2,578

Advert