Hi Forum.
First post cos this has me scratching my head.

We have 3 single phase boards on an installation in edinburgh.
All 3 boards have tested fine and been certified as so.

However, we have been called back as one board keeps tripping when a hoover is plugged in.

There is a 30mA RCD as the main switch and this problem only occurs when the hoover is plugged in to either ring on this board. we have tried 2 different hoovers on this board and both trip the RCD but none of them trip the RCD on the other 2 boards. We have even tried an electric drill on the tripping circuits but it runs fine??????
Do vacuum cleaners leak much current?
Any help appreciated.
 
If you have a ramp test function, try that too. might show up as an RCD on its way out. This will give you the trip current rather than the time..........
 
Hi Forum.
First post cos this has me scratching my head.

We have 3 single phase boards on an installation in edinburgh.
All 3 boards have tested fine and been certified as so.

However, we have been called back as one board keeps tripping when a hoover is plugged in.

There is a 30mA RCD as the main switch and this problem only occurs when the hoover is plugged in to either ring on this board. we have tried 2 different hoovers on this board and both trip the RCD but none of them trip the RCD on the other 2 boards. We have even tried an electric drill on the tripping circuits but it runs fine??????
Do vacuum cleaners leak much current?
Any help appreciated.


Sounds as if it is nothing to do with the hoover, could check this by trying something else with a big load (kettle, toaster). I guess you have an earth leak to neutral of something under 30 ohms, and plugging the hoover in causes the voltage on the neutral to go to 1 or 2 volts which then leaks down the leak giving you 1v/30 ohm = 33 milliamps leak.

I'd start by switching off the main switch on the offending board and measuring neutral - earth resistance without unscrewing anything. If it is over 1 Megohm then I'm wrong and you need another idea, if under then chase it.

But remember to turn off the main switch otherwise you are just measuring the n-e resistance on next door's pme connection. You can feel really silly after getting this one wrong - I did.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD Tripping Problem
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
thearabstrap,
Last reply from
Matthew M,
Replies
5
Views
6,345

Advert