Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.
 
Can anybody help... Went to a job Friday where apparently RCD is coming out once every couple of nights. The rcd covers 4 circuits which are sockets, sockets, heating and outdoor shed. I have carried out a blanket test and I am getting a reading of about 20M This is with loads conncted apart from 2 neon extension leads which if connected brings it down to 0.39M.(still to high to cause tripping). I have also done a ramp test on rcd and it comes out at 23mA. Finally put clamp meter around tails serving rcd and with loads connected was still only getting 10.5mA of earth leakage. Thanks for any advice.

what kind of loads are connected
 
Washing machine, freezer, electric fence fed from shed, kettle, boiler. Even ran up heating but earth leakage still didn't go above 10.5mA. Did mention fitting rcbo's but if its an appliance breaking down this wouldn't help( just cause more expense).
 
Would if I had some..
 
From your testing the circuit wiring seems OK, therefore you are now heading for connected equipment with an intermittent fault, always a nightmare.
You probably need to do some investigation of the times and weather conditions when the RCD trips. If the trip is over night then it is only likely to be items that are running overnight.
Because some of the items are outside it could be water ingress, since you have 10mA already you only need another 13mA to trip it.
Could the electric fence be shorting when something pushes against the fence.
Freezers can be prone to tripping RCDs when old, less likely, but maybe you could run the freezer on an extension lead from another circuit for a few nights and see if the other circuit trips.
Did you run the ashing machine as these often break down to earth, but only when X item is activated, do they run the machine overnight?
 
Seems lot of stuff in the outdoors there..!!
I'd be looking there first to eliminate them from my enquiries..
 
electric fence on an rcd is an interesting idea, touch the fence i bet it trips the rcd
 
freddie the fox strikes again.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCD Tripping.....
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
10

Advert

Thread statistics

Created
dlt27,
Last reply from
telectrix,
Replies
10
Views
3,336

Advert