Good morning all. So question; if you’re making additions to an existing circuit, but the new cable is not min 50mm deep in wall or mechanically protected and the current circuit is not RCD protected do you tell customer that RCD protection is required as per the regs? My thought is yes and explain why it’s needed to customer; if they don’t want it then I’d walk away but just want to hear others views. TIA
 
So adding 3 new double sockets in to existing ring but one of the sockets in the wall cannot go 50mm deep. Oval conduit isn’t really mechanical protection.
 
Yep, there the option for that possibly. My post was really to answer a question I had with another spark about some work being done. My view was it needs either proper mechanical protection (metal conduit) or (a future proof measure) RCD protection.
 
For me, with the new regs I always where applicable advise customers about the need for RCD protection. Some jobs I win, some I lose as there’s always someone willing to just wire it up and then throw smoke.
 
I wonder what the scams view point is working on an older non rcd installation and not adding in any rcd protection..?
 
same as all of us.all new sockets added require RCD protection, even if the existing sockets are not. e/g. feed new sockets via a RCD FCU. if not protecting the whole circuit.
 
this cheesecake was over 4 tons. might last spoon a while
50266
 
I wonder what the scams view point is working on an older non rcd installation and not adding in any rcd protection..?

I was doing kitchen refurb, where the client had a couple of FCU’s and wanted to replace them with socket outlets (no rcd protection).

I asked my scheme, if that would be classed as ‘maintenance’? I got a ‘stupid boy’ sigh, and told no it’s not.
 
Probably cuz they aren't sure, or don't know what to do next. To which I suppose begs the question, do the Schemes know the answer any way, replies on a post card please. Someone said "A stupid boy sigh" says it all really.
 
Last edited:
Probably cuz they aren't sure, or don't know what to do next. To which I suppose begs the question, do the Schemes know the answer any way, replies on a post card please. Someone said "A stupid boy sigh" says it all really.

In fairness to them, the Tech Support of my Scheme were quite knowledgeable, thorough with their replies, and from the experience & qualifications they held (as seen from editorials on them), I was in no doubt of their qualified answers. There was a particular individual, whom I wasn't sure about, the rest were exemplary.

When you consider, when you ring in with a query, the guy would respond straight away with his guidance quoting regulation numbers etc, its not like replying to a thread here, with the advantage of time, browsing regs book or using Google. They were most helpful.

I don't think you can criticise something, without the experience of using it.
 
It's Friday... I have my popcorn at the ready...
 
My daughter just bought a house...went and had a look on Saturday...new extension built 6 months ago,,,new lighting and ring final circuits to extension and kitchen......Metal sockets..metal switches no sign of an RCD anywhere......looked up the details on the BC website and a electrical notification was sent by the company that done the work.....description.....work carried out in a special location...new circuits..........Found the company on line registered FULL SCOPE NIC..............On the phone tomorrow morning
 

Reply to Requirements for RCD protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
885
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
607
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
989
Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock