So you have the option of reinstating the RFC or just disconnecting both ends of one leg.

Why not reinstate what is there leaving no cables loose in the back of a socket or DB. What happens when they decide to start plugging more appliances in, as believe me customers dont always tell the truth about what they have plugged in.
 
Surely if it's just stated happening there could be a fairly easy to pinpoint problem?
 
So you have the option of reinstating the RFC or just disconnecting both ends of one leg.

Why not reinstate what is there leaving no cables loose in the back of a socket or DB. What happens when they decide to start plugging more appliances in, as believe me customers dont always tell the truth about what they have plugged in.

charge them again for changing it back to a ring ;-) haha
 
  • Like
Reactions: 1 person
One other thing OP have you done your cable calcs for volt drop and worked out if the Zs value will be compliant?
 
  • Like
Reactions: 1 person
One other thing OP have you done your cable calcs for volt drop and worked out if the Zs value will be compliant?

Pah.... making a right meal of it. Would you really sit there doing cable calcs for this?? I wouldn't. He can go at least 2.40 Zs on B16 60898. Experience would tell you, fit MCB and derate to radial, Quick Zs, MW, Done.
 
  • Like
Reactions: 3 people
One other thing OP have you done your cable calcs for volt drop and worked out if the Zs value will be compliant?

You've saved me asking.

But for a Electrical Trainee what does that matter, he’s got the cash in his pocket and ridden off in to the sunset.
 
  • Like
Reactions: 1 person
Pah.... making a right meal of it. Would you really sit there doing cable calcs for this?? I wouldn't. He can go at least 2.40 Zs on B16 60898. Experience would tell you, fit MCB and derate to radial, Quick Zs, MW, Done.

Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.
 
You've saved me asking. He’ll be bloody lucky if it’s compliant.

He'd be bloody unlucky if it wasn't compliant!! Lighting Zs on 1mm 6242 in a house is very rarely over 1.50 Zs, this is 2.5mm. Real world.
 
Last edited:
  • Like
Reactions: 1 person
Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.

Charging unnecessary time is lining your pockets. Using your experience to save a customer money is not.
 
  • Like
Reactions: 1 person
Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.

Something wrong with your eyes :54:Dillb?
 
  • Like
Reactions: 1 person
wye eye, as geordie would say
 
  • Like
Reactions: 2 people
Then what happens if the Zs and volt drop are not compliant?

Who pays then?

On a serious note though, you make a valid point, but chances are if VD and Zs are ok on the old ring, they'll be ok on a lower rated radial.

This is not an excuse not to check though.

Though. Just thought I'd throw in another though as two didn't seem samey enough, Lol.

And another lol in case Eng 54 is reading! lol.
 
  • Like
Reactions: 1 person
Then what happens if the Zs and volt drop are not compliant?

Who pays then?
Even if Zs was a bit over for MCB, which it almost certainly won't be, I would have no problem in utilising the 30ma RCD to provide satisfactory earth fault disconnection in this instance. This is not designing new circuits, this is getting someone up and running when they have a problem.
 
Here you go Voltz, I thought you might like to use this for your Avatar.
 

Attachments

  • I-must-correct-you-anyway.jpg
    I-must-correct-you-anyway.jpg
    40.8 KB · Views: 97
  • Like
Reactions: 1 person
Even if Zs was a bit over for MCB, which it almost certainly won't be, I would have no problem in utilising the 30ma RCD to provide satisfactory earth fault disconnection in this instance. This is not designing new circuits, this is getting someone up and running when they have a problem.

Pure laziness. Besides what happens if the RCD fails?

Replace the faulty leg get it back to how it was before and get paid.
 
  • Like
Reactions: 2 people
Pah.... making a right meal of it. Would you really sit there doing cable calcs for this?? I wouldn't. He can go at least 2.40 Zs on B16 60898. Experience would tell you, fit MCB and derate to radial, Quick Zs, MW, Done.

oh my god. Exactly what I was going to say. Absolutely ridiculous. Some on here just look for holes and use that to flex their BYB muscles.
 
Well yes I would and I am pretty sure most others on here would do too.

Anyone that doesnt design every circuit they install is in my wyes just a chancer that thinks of nothing but lining their own pockets.

Crap. You are obviously out of practice.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Ring to radial
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
59

Advert

Thread statistics

Created
AdieB,
Last reply from
Knobhead,
Replies
59
Views
4,226

Advert