Hello Guys


I'm going to put my Tin hat on and close the curtains so the Regs police can't arrest me for asking this question again, I can only find old threads pre 18th edition so please advise me if I'm missing something


I've just been watching a guy on Youtube doing a board change who's said that to comply with the 18th edition of the Wiring Regulations you must seal ALL entry holes into a consumer unit regardless of them coming through the bottom, top, sides or rear entry with a suitable intumescent mastic to stop the spread of fire into the fabrication of the building!!!


I personally am NOT aware that anything changed in the 18th Edition to say all entry points have to be fire sealed I've been looking online tonight and can only find write ups from "Wiring Matters"

Stating


Sealing of wiring entries
It is important for the installer to seal all openings into the enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables - see Figure 6. The intent of the sealing is to ensure that, as far as is reasonably practicable, any fire is contained within the enclosure or cabinet and the escape of flames to the surroundings of the cabinet or enclosure or into conduits trunking or ducting is minimised, as intended by Regulation 421.1.201.
Good workmanship and proper materials must be used, and account must be taken of the manufacturer’s relevant instructions, if any.


Regulation 421.1.201 Does not mention sealing any apertures in a consumer unit with, grommets, glands or sealant and does not mention that the Metal clad board cannot be fitted to a timber backboard. So why is the IET saying we are to be sealing the holes , personally I've been installing all my boards with cables entering from behind and mounting my boards on the existing wooden backboards using a length of stick on trunking as a framework around the consumer unit.


Am I wrong???
 
NIC man said to me he didn’t want to see any wood. Top needs to meet IP 4X the rest IP 2X
 
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.
 
  • Like
Reactions: buzzlightyear
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.
The plastic rawlplug was brought up at my last assessment, there’s no concern over them as the wall they’re in will support the clips or consumer unit.

This idea of sealing up all the opening with intumescent sealant seems another cash generator to subsidise the cost of changing to metal consumer units
 
  • Like
Reactions: JK-Electrical
When this reg first come out, the guidance was only ‘seal’ to the appropriate IP rating as previously mentioned. Then Wylex started flogging intumescent bags to go inside their CU’s, then the grown ups at the IET came out with that crap about contains a fire etc.

On my very last assessment two years ago, my Elecsa assessor suggested just to follow the IP rating, and don’t worry about mounting on wood.

I suspect the next thing, will be not to use plastic raw plugs to fix the CU to none flammable structure.

If you will the CU up with water then they never catch fire..... Job done...
 
Of course water will stop the spread of fire, the CU would need to be IP65 rated to hold the water though:)

You put the water in a plastic bags, silly..... Then when there is a fire the bags burst and put out the fire....
 
You put the water in a plastic bags, silly..... Then when there is a fire the bags burst and put out the fire....
You must work for the London Fire Brigade, what a fantastic idea because the water would then trip the rcd’s and would make the house dead!!
 
Reading the last few posts,it is not wise
I now fear the Iet will take up this combined fire prevention and power isolation strategy
We should be wary of giving ideas to the folks making up the think tank
 
That guys a roaster. Shoves wago boxes in ceilings and reckons they are MF - not the way he does em, they aren’t.
He makes out he’s experienced but often says things that suggests he’s a newbie.
Ignore his ideas.
 
  • Like
Reactions: suffolkspark
That guys a roaster. Shoves wago boxes in ceilings and reckons they are MF - not the way he does em, they aren’t.
He makes out he’s experienced but often says things that suggests he’s a newbie.
Ignore his ideas.
Who you talking about hope your not talking about me that’s certainly not my workmanship
 
I’m talking about the YouTube guy you referred to
 
  • Like
Reactions: DPG
Are we talking about CHris the handyman youtuber sparky plumber builder Tiler plasterer gezza man

 
Last edited by a moderator:
Is it Penry, the mild-mannered janitor?
 
Cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than: · 1.0 mm for the horizontal top surface and · 2.5 mm for all other surfaces of the enclosure that are accessible after installation. For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above. Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
 
Cable access into the metal consumer unit must maintain the integrity of the non-combustable consumer unit so far as reasonably practicable. This can generally be achieved by the installer ensuring that cable access holes they make in the enclosure do not to leave gaps greater than: · 1.0 mm for the horizontal top surface and · 2.5 mm for all other surfaces of the enclosure that are accessible after installation. For rear cable access, the minimum number of knockout(s) shall be removed and a cable protector fitted; see illustration above. Tests on hager consumer units have indicated that there is no specific need for external fire rated cable glands or intumescent sealing in addition to the guidance below, with respect to achieving a non-combustible enclosure. However this does not preclude the designer/installer from using fire rated cable glands or external intumescent sealing should they consider necessary. Internal intumescent pads shall not be used.
well done Charlie I could not put it better me self .
 
  • Like
Reactions: Charlie_

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bury

Thread Information

Title
Sealing a consumer unit entry points??
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
128

Advert

Thread statistics

Created
leebut,
Last reply from
Simon47,
Replies
128
Views
61,706

Advert