Hello,
I need to install a type 1+2 SPD into the main panel of a small business building, which needs lightning protection.
The main breaker in the main panel is a 4 poles 40A MCB.
I was looking for a SPD and I found this: Schneider A9L16634.
In the technical specification sheet it says "Associated circuit breaker NG125N 80A curve C - Icu 15 kA".
I was wondering why the associated breaker needs to have such a high current (80A)? It seems i cannot ensure the selectivity of the breakers.
Could anyone explain what can happen if i use a smaller breaker, for example a 32A one for the protection of the SPD?
Thank you.
If it is a Type 1 it is probably designed to be at the source (intake).
If your board is protected by a 40A MCB it sounds like a secondary dist board, where just a type2 might do?
Generally follow manufacturers advice.
Perhaps the board you are using doesn't have 32A breakers with sufficiently high short circuit breakage capacity (kA)?
If a breaker is used with insufficient capacity it may be damaged in the event of a surge and not disconnect properly resulting in damage to equipment you are trying to protect?
Reply to Selection of MCB for SPD protection in the UK Electrical Forum area at ElectriciansForums.net
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Hi, now everything is SPD's I've been told they need to be on their own MCB. So incoming line goes through the main switch then busbar then MCB...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...