Matters not. I am not saying up the breaker.....but if you do up it, the cable should also be upped accordingly for cable protection. That protection is needed, even though you are not varying the load. Just regulation, that's all.
The regulations specifically allow omission of fault protection where the circuit is not expected to be able to carry overload current so you can have a situation where say a fixed load is 46 amps the ccc of the cable is 48 amps but your ocpd is 50 amps provided fault protection is afforded as required by section 434
The formula for the tabulated current becomes Ib/correction factors rather than In/
The regulations specifically allow omission of fault overload protection where the circuit is not expected to be able to carry overload current so you can have a situation where say a fixed load is 46 amps the ccc of the cable is 48 amps but your ocpd is 50 amps provided fault protection is afforded as required by section 434
corrected that for you.no charge. otherwise i agree, as long as the Iz > Ib.
OK then. The circuit is in place, whose to say the load won't be increased in the future?
That's not how you design a circuit though. After all the shower could be removed and a new sub CU installed at the end of the cable if the use for the room changes.
If the load changes, the circuit design changes and protection and cable size should be altered to suit.
Reply to Shower tripping mcb after being used in the UK Electrical Forum area at ElectriciansForums.net
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Went back it a house after they upgraded shower to a 9.8kw, pulling 40a constant. We had wired it with 10sq and 40a RCBO. 10sq Neutral cable...
Can i just check something. If a rat decides to chew a cable will it trip the MCB or RCD ? I ask because I had one house recently that had a...
90s house electric issues continues 🥲 So after getting some good advice here I've managed to sort out some of the heating issues so thank you...
I have a 32amp MCB for my heating (heat pump) and when the heating comes on, it trips after a few seconds. If I push it back up it works fine...