rhys24

Hi

Been working through a few options with an electrician, on how to get an 4 way db to supply some new equipment being installed.

Due to the original board being pretty full up, they don't want to split a henley block out of it. As its only 100amp board and pretty loaded up already.

So suggested this.

Run from where the mains come into the property 25mm 3 core onto the new 4 way board with 100a switch. Due to the location of this its going to need about 40-50 meters of cable and I know its not cheap!

That was the first options, upon discussing with a few other people suggested this:-

Just splitting the power before the distribution board in the property then running to the new db and the old board. Would this be any difference?

As I guess the breaker in the ryefield box would be 100 amps?

The other challenge, is that the main fuse for the property as its a london apartment is locked up in ryefield box which is locked. What's the correct way to get access to this box? It has an edf sticker on it.

Any suggestions would be great!

Thanks
 
You can split the tails in a Henley and have more than one CU unit.....no problem at all with that. If you want to run one set of tails over 3m then you'll need to fuse them down (80amp fuse if main fuse is 100a).

You don't say what the load will be on the second DB, if it's not gonna be much you could just run a sub-main from existing DB, I know you said it was pretty full, but would only need one spare way.

As for access to the box.......crowbar?????? :)
 
Hi

Been working through a few options with an electrician, on how to get an 4 way db to supply some new equipment being installed.

Due to the original board being pretty full up, they don't want to split a henley block out of it. As its only 100amp board and pretty loaded up already.

So suggested this.

Run from where the mains come into the property 25mm 3 core onto the new 4 way board with 100a switch. Due to the location of this its going to need about 40-50 meters of cable and I know its not cheap!

That was the first options, upon discussing with a few other people suggested this:-

Just splitting the power before the distribution board in the property then running to the new db and the old board. Would this be any difference?

As I guess the breaker in the ryefield box would be 100 amps?

The other challenge, is that the main fuse for the property as its a london apartment is locked up in ryefield box which is locked. What's the correct way to get access to this box? It has an edf sticker on it.

Any suggestions would be great!

Thanks


Are you sure you dont mean the ISO switch will be 100A????? The ISO is not an mcb (breaker)!!!

I would also run the 25mm 3 core swa through a switch fuse.
 
Yes sorry Didn't mean to say breaker!

Second box would have just 2 x 32amp breakers. The first CU counting up all the breakers has 248amp in total.

I would also run the 25mm 3 core swa through a switch fuse. Something like this LINK

Apart from the crowbar :o_O: who should have the key? or is it a key that can just be requested as lost and replaced? As I don't really want to have to arrange any supplier out to just open the box and disconnect it!
 
Yes sorry Didn't mean to say breaker!

Second box would have just 2 x 32amp breakers. The first CU counting up all the breakers has 248amp in total.

I would also run the 25mm 3 core swa through a switch fuse. Something like this LINK

Apart from the crowbar :o_O: who should have the key? or is it a key that can just be requested as lost and replaced? As I don't really want to have to arrange any supplier out to just open the box and disconnect it!


Yes to the switch fuse!!!
 
Hi

Been working through a few options with an electrician, on how to get an 4 way db to supply some new equipment being installed.

Due to the original board being pretty full up, they don't want to split a henley block out of it. As its only 100amp board and pretty loaded up already.

So suggested this.

Run from where the mains come into the property 25mm 3 core onto the new 4 way board with 100a switch. Due to the location of this its going to need about 40-50 meters of cable and I know its not cheap!

That was the first options, upon discussing with a few other people suggested this:-

Just splitting the power before the distribution board in the property then running to the new db and the old board. Would this be any difference?

As I guess the breaker in the ryefield box would be 100 amps?

The other challenge, is that the main fuse for the property as its a london apartment is locked up in ryefield box which is locked. What's the correct way to get access to this box? It has an edf sticker on it.

Any suggestions would be great!

Thanks

Get another sparky in!

EDF??

Are you sure the chap you had in is actually a sparky?
 
Last edited by a moderator:
Henley block to a switch fuse. SWA to new board.
do your cabe calls for the SWA size as it may not need to be 25mm, fuse the switch fuse to suit your load required.
as for adding up the breakers in a board forget that as it doesn't work that. Remember a small word called diversity ( and that not the dance group)
 

Reply to Splitting Incoming Supply. Question & Ryefield access. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just looking for advice. Ive been to look at a Fire alarm install job. While checking where i will take my supply from. 3 phase sub board, i...
Replies
20
Views
1K
We are refurbishing an empty commercial building at the minute and I don't do commercial stuff day in day out so not entirely clued up on...
Replies
11
Views
1K
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
470
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock