Sorry I was expecting to see a zone valve. The pipe with the bonding clamp on it does that go to UFH manifold and the pipe going up is flow for upstairs rads ?. To be sure what the pipes go what is the boiler ?.
 
This is the view I have, the manifold is on a board under the boiler. There is also the only view I have of the boiler etc, I think the pump is tucked away above this lot.

IMG_4537.JPG
 
The pipe to the manifold comes from that U bend seen in the above post... i've got a picture but it's literally just one dusty pipe behind that board so it must be.
 
I think that the pipe which is a Y shape ie comes from boiler splits down to the UFH up to rads is heating flow (what boiler is it) a 2 port valve would need to be put in the leg that goes to rads (after split).Have you got a photo of UFH control unit.
 
I think that the pipe which is a Y shape ie comes from boiler splits down to the UFH up to rads is heating flow (what boiler is it) a 2 port valve would need to be put in the leg that goes to rads (after split).Have you got a photo of UFH control unit.

It's a combi. The UFH is an Emmeti ewc-1... i've got this picture but access is cramped here.

IMG_4490.JPGIMG_4490.JPG
 
boiler.jpg You will have to get a plumber to check what combi is it ?
 
In the boiler for the heating you should have terminals for a stat eg L and Rt from stat a two core & E cable/flex would need to be connected between this and the volt free boiler terminals in UFH wiring ctr. when a valve is fitted to leg for rads the orange and gray will go between the room stat terminals in the boiler. The brown to open the valve goes to 3 in the wireless stat link between live and 1.
 

Attachments

You could try backing the flow control valves back on each of the UF manifold zone valves effectively starving the ground floor and forcing flow to the rads. Ideally move the stat upstairs. This will require a lot of tinkering with flow rates but may at least get you some heat upstairs in the short term.

As already said the real answer is to split the zones.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Burton

Thread Information

Title
Splitting of UFH and Rads via Stat
Prefix
N/A
Forum
Electric Underfloor Heating Wiring
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Mason Carter,
Last reply from
Toneyz,
Replies
24
Views
5,427

Advert

Back
Top