I've installed a garage consumer unit sub-main to an outbuilding in 16mm 3 core armoured, the insulation tests all come back fine - +800Mohms on a 500 volt test but when I power up the installation I get 90 volts leaking to Earth from Neutral and i'm not sure why. The Garage RCD also doesn't trip on the test button.

The circuit goes from a 32A mcb protected by RCD in the House Consumer Unit, in 10mm t&e to a 63A Rotary Isolator inside the house, then from the Rotary Isolator to the Garage Consumer Unit in 16mm Armoured run underground in Copex ducting.

The voltages at the Rotary Isolator are fine - 230V between L-N and L-E and 0V Between N-E.

Once the circuit is live, there's a 90 volt Leak to Earth from the Neutral, somewhere starting at the Rotary Isolator up to the Garage Consumer Unit.

The Copex has water in from the heavy rain recently so no doubt the armoured is partially submerged but surely any problem would show up on the insulation test?

The only thing I can think of is that the Isolator is faulty so when I next go back i'm going to bypass it and see if he fault clears.

Apart from that i'm out of ideas, anyone got any thoughts?

Cheers
 
the insulation tests all come back fine - +800Mohms on a 500 volt test but when I power up the installation I get 90 volts leaking to Earth from Neutral and i'm not sure why.
What tester are you using when you see the 90 volts? Make the same test again using either an analogue tester or a digital tester with a 'Lo-Z' facility.

Here's one of the many past discussions about ghost voltage;
 
90 volts leaking to Earth from Neutral

Sorry, this doesn't quite make sense. Neutral is already near earth potential. Do you mean: "There is a leak from line that raises the neutral conductor to 90V from earth?"
If so, then yes, the leak is probably normal capacitive leakage but the neutral conductor is not solidly connected to neutral because of a bad contact in the isolator. Any significant voltage on a neutral conductor especially when unloaded, indicates a faulty connection upstream.
 
I returned to the job this morning and the fault had cleared on it's own and everything tested out fine and works now so i'm not sure what was causing the voltage to appear.

Thanks for the replies though, I learned some things.
 

Reply to Strange N-E fault on armoured cable supply to sub-main in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Replies
3
Views
1K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
426
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
695

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock