Reaction score
7,757
been out to test a 1st floor flat and all the sub mains and meters are in a hall way ground floor going to each flats which are 5, the sub mains are not rcd protected ,i guess when it was converted and tested to the 16th or there about . can not see how it was installed so the building belongs to who ever , having the sub main going to that flat and owner owns that floor , ,i have c2 it not having rcd protection reg 522.6.203 .
 
been out to test a 1st floor flat and all the sub mains and meters are in a hall way ground floor going to each flats which are 5, the sub mains are not rcd protected ,i guess when it was converted and tested to the 16th or there about . can not see how it was installed so the building belongs to who ever , having the sub main going to that flat and owner owns that floor , ,i have c2 it not having rcd protection reg 522.6.203 .
What cable is used Buzz?
 
I've only ever done this in SWA but you do end up with the problem of presenting it neatly into a domestic CU downstream.
 
it could be argued that the cable runs themselves are covered by the 'skilled persons' get-out clause because no-one except a contractor instructed by the landlord is going to be drilling through walls in communal construction. Maaybe.
 
It is likely that it was compliant at the time of installation, a code 2 would only be appropriate IMO if it could be ascertained that there was a real possibility of disturbance or mechanical damage. If not I would apply a code 3.

it could be argued that the cable runs themselves are covered by the 'skilled persons' get-out clause because no-one except a contractor instructed by the landlord is going to be drilling through walls in communal construction. Maaybe.
it like what comes first chicken or the egg job .
 

Reply to SUB MAIN IN FLATS in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
441
Hi everyone, Got a job converting commercial property into 4 flats, 2 up 2 down all with electric meters on the outside on ground floor, SWA to...
Replies
0
Views
630
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock