Hoppy, This is what I would do. Buy a 60A KMF. Feed with tails from Split Henley and you can then terminate your 16mm T&E correctly and ensure it is fused correctly. Fill in a MW saying replaced damaged unit like for like. Don't bother adding RCD at the front, if it was to be added in future it would be much better to RCD / RCBO at DB2 where the protection could be split up amongst final circuits.
 
Hoppy, This is what I would do. Buy a 60A KMF. Feed with tails from Split Henley and you can then terminate your 16mm T&E correctly and ensure it is fused correctly. Fill in a MW saying replaced damaged unit like for like. Don't bother adding RCD at the front, if it was to be added in future it would be much better to RCD / RCBO at DB2 where the protection could be split up amongst final circuits.

i like it. sometimes you can go too far trying to get older installations up to today's regs.
 
Hi,

been to job today to install a new bathroom light & fan in a HMO.

The 1st & 2nd floors are fed via a second db on the first floor - db2.

DB 2 is fed using 16mm twin, buried approx. 2m in wall, it is connected to the main tails next to db1 at the intake position, via Henley blocks, so single core insulation exposed (C2 as in kitchen cupboard used for plates etc). DB2 has 100A main switch and mcb's -no RCD protection. DB1 has a 63ARCCB Main switch.
Anyway not doing EICR yet, that is coming though.

My question is, when the EICR is completed it is going to fail due to the 16mm twin being protected by the 100 main fuse, so this will need rectifying, what would you do. Install an RCD unit which would mean a full test on DB2, or Is it ok to install a 2way enclosure with a 63A MCB, but would you still have to do a full test on DB2, or could you just test the sub main.
Not sure if it is acceptable to just protect the cable with an mcb, as I am not doing anyway work on the sub main.
The work I did in the bathroom is protected by a B6 60898, and I have installed an RCD FCU, to cover the light & fan!

Thanks!

Hoppy, This is what I would do. Buy a 60A KMF. Feed with tails from Split Henley and you can then terminate your 16mm T&E correctly and ensure it is fused correctly. Fill in a MW saying replaced damaged unit like for like. Don't bother adding RCD at the front, if it was to be added in future it would be much better to RCD / RCBO at DB2 where the protection could be split up amongst final circuits.

A light and a fan.
The total cost to cover up not doing basic checks beforehand will be?
 
In domestic you cannot achieve S/C discrimination and very little partial discrimination, you can usually match your fuse to the DNO as they tend to use a type III or IV against your typical BS88 II so overload discrimation is in your favour.
 
Please tell me this isn't a serious reply.

It is a serious reply.

As I understand it, to achieve discrimination under fault conditions, the pre-arc I²t of the higher rated fuse has to be less than the total I²t of the lower rated fuse. Looking at one manufacturer's data for BS88 fuses, it appears that for the ratings we're considering, you need the rating of the smaller fuse to be less than 50% of the larger one, or thereabouts. So, as darkwood says, difficult to achieve in this sort of application.
 

Reply to Sub main protection! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Replacing DB’s with all singing all dancing RCBO’s Problem’s we have now…Existing installation consisted of DB Grd Floor.. DB 1st Floor…Grd Floor...
Replies
11
Views
1K
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
819
Hi, I have been tasked with a kitchen rewire. The current DB is fed by a 16mm armoured. There is a split load old contactum DB which I don’t...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock