Discuss TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

AdieB

-
Reaction score
6
Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way above the 0.8 Ohms. Cleaned up the earth clamp and tightened it up and improved the reading to 1.7 Ohms. Tested from the live in the fuseboard to the lead sheath of the incoming supply with no earths attached and again achieved 1.7 Ohms. As this Ze value is the best that can be achieved what is my next action. Contact the local DNO and ask them to sort it, or Install an earth rod and change to TT system. This has obviously happened before top some body. Anyone help ------PLEASE.
AdieB
 
Testing at a house today. The supply is a TN-S. Earth taken from lead incomer cable. First test with my Megger 1730 gave me Ze of 3.5 Ohms, way above the 0.8 Ohms. Cleaned up the earth clamp and tightened it up and improved the reading to 1.7 Ohms. Tested from the live in the fuseboard to the lead sheath of the incoming supply with no earths attached and again achieved 1.7 Ohms. As this Ze value is the best that can be achieved what is my next action. Contact the local DNO and ask them to sort it, or Install an earth rod and change to TT system. This has obviously happened before top some body. Anyone help ------PLEASE.
AdieB

Yes call the DNO. It's their earth and they have to maintain it. Don't start making this into a TT, you only need to consider this when no reliable earth has originally been supplied.
 
Bang an RCD in and you will be fine, in the mean time you could contact the DNO and ask them to improve the reading, 1.7 ohms isn't the end of the world and far better than a pin in the ground giving a 30 ohm reading lol.
 
OP gives a possible insight. " tightened the clamp" . was this then a DIY TN-S?
 
The house is in a residential area. The clamp is an old type which goes around the sheath of the cable with a nut and bolt either side it was slightly loose. I also re-sited it on the cable as did not want to keep tightening and then go bang, this achieved a better Ze. The clamp is fit for purpose just old. There is a 17th edition fuseboard with 100Amp main switch and then two separate RCD's controlling 6 and 4 ways respectively.
 
The house is in a residential area. The clamp is an old type which goes around the sheath of the cable with a nut and bolt either side it was slightly loose. I also re-sited it on the cable as did not want to keep tightening and then go bang, this achieved a better Ze. The clamp is fit for purpose just old. There is a 17th edition fuseboard with 100Amp main switch and then two separate RCD's controlling 6 and 4 ways respectively.

Well what do you think then?
 
I think the DNO should come out and improve the reading. But as I said when I tested from the live in the fuseboard and the sheath of the incoming cable the best I could achieve was 1.7 Ohms so I cannot see how they could give me the required 0.8 Ohms. This is why I have asked the question to see if someone has had this problem before and solved it or advise as to the best way forward.
 
I think the DNO should come out and improve the reading. But as I said when I tested from the live in the fuseboard and the sheath of the incoming cable the best I could achieve was 1.7 Ohms so I cannot see how they could give me the required 0.8 Ohms. This is why I have asked the question to see if someone has had this problem before and solved it or advise as to the best way forward.

But what you cant do is to check the connection back at the sub station can you. Call the DNO, they have a responsibilty to ensure the Ze is within regs.

And yes I have had this on a number of occasions and Western Power sorted it out
 
Yes call the DNO. It's their earth and they have to maintain it. Don't start making this into a TT, you only need to consider this when no reliable earth has originally been supplied.
yes...rodding it will give no real advantage here.....it would be unlikely that TT would give a similar value....and as you say...its distributer earth...so they can sort it....
 
As TaffyDuck has already said fault could be anywhere between mains intake position and sub station. Fault could easily rise way above existing 1.7 ohms. Get DNO out to it. Generally find they respond very quickly to earthing faults on distribution system. Generally couple of hours max.
 
As TaffyDuck has already said fault could be anywhere between mains intake position and sub station. Fault could easily rise way above existing 1.7 ohms. Get DNO out to it. Generally find they respond very quickly to earthing faults on distribution system. Generally couple of hours max.
but he needs to get put straight through to the duty engineer....
not some dopy, obnoxious bint on the end of the phone....
 
Bang an RCD in and you will be fine, in the mean time you could contact the DNO and ask them to improve the reading, 1.7 ohms isn't the end of the world and far better than a pin in the ground giving a 30 ohm reading lol.

So if you were to put RCDs in to meet disconnection times on a TN system that doesn't meet maximum Zs, what I wonder is the position then with certificating the work, particularly in terms of the should-virtually-always-say-None "Deviations from BS7671" box? I know it'd be kosher on a TT system as you have little choice, but on a TN system where Zs is above max...
 

Reply to TN-S high Ze in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening Chaps As can be seen in the attached photo , the incoming supply cable has a Earth soldered to the outer sheath of the cable suggesting...
Replies
10
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi, Any suggestions what this black cable is coming off the supply's incoming cable? Its a TN-S system, I thought it could be the earth conductor...
Replies
29
Views
3K
I have come across what I think is a looped supply - like a normal incomer but two of them coming up side by side. It's a TN-S arrangement with an...
Replies
12
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock