It is interesting that the non discrimination is shown as a type S 100mA RCD tripping in 100ms at 60mA, which does seem a very poorly designed RCD since the minimum time delay should be 150ms and the RCD should not trip until 100mA (though it is likely to trip earlier, 60mA seems a bit low)
60ma does seem low. But when ramp feasting 30ma RCDs I find it can range between 17ma-25ma with out going load disconnected.
I have fitted a few of these 100 ma s type RCDs recently with 30 ma further down stream on a farm. I may be going back, pretty soon so I could ramp test it and check tripping time and post the results
 
Doesn't really matter whether you fit a 100mA or 300mA S type to be honest on a TT system, as additional back-up for 30mA RCDs downstream. What i will say, is of what must be by now, the many hundreds (if not more) of times we have used 100mA S type RCDs for discrimination purposes for downstream 30mA units, i can't remember ever having problems such as been described in this article!!

I must have a more in-depth read, as i haven't had that must time these past couple of days, and have only had a quick over-view....
 

Reply to TT earthing and supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
877
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
606
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock