60ma does seem low. But when ramp feasting 30ma RCDs I find it can range between 17ma-25ma with out going load disconnected.It is interesting that the non discrimination is shown as a type S 100mA RCD tripping in 100ms at 60mA, which does seem a very poorly designed RCD since the minimum time delay should be 150ms and the RCD should not trip until 100mA (though it is likely to trip earlier, 60mA seems a bit low)
I have fitted a few of these 100 ma s type RCDs recently with 30 ma further down stream on a farm. I may be going back, pretty soon so I could ramp test it and check tripping time and post the results