Hi all,just started using this forum,amazed theres so many people on it.

I have to change a board on a TT system(haven't done one before).
The cpc looks to be around 6mm(not sure untill i test it wether to change it to a 16mm),and has an old rccb protecting a wylex db.

Can I use a 17th dual rcd board or do I have to use a normal board with rcbo's?
Also am I right in saying that the Ze has to be below 200 ohms and the Zs for each circuit 1667 ohms.

Appreciate any advice

Thanks All
 
Welcome along.
:D
As this is the introductions thread, try posting your querey in the relevant section of the forum.

You will get more views and replies there.
 
Do you mean the main earth looks to be 6mm??
If so and it is not burried in the ground it is probably ok. 16mm if burried.

Yes you should aim for your Ze or rod Ra to be as low as poss.
Although the regs state that for a 30mA Rcd the max is 1667.

You could fit either db, I would be tempted to replace the main switch in either with a 100mA type s Rcd. (Time delay) for extra protection. Not required.
Personally rcbos is a better job but a lot more money.

Hope this helps
 
Hi & welcome.:)
 

Reply to tt systems in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
880
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
Big argument with a newly qualified electrician with all the necessary qualifications Had to give him a hand later on during the day, nice DB...
Replies
12
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
968
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock