In domestic when the Zs easily low enough why do we default to have type B instead of C curve MCB's/RCBO's
 
CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
N

Nigel

  • Thread Starter Thread Starter
  • #7
Ok. Not soley for domestic but you know what I mean.

There is little in a domestic that requires a Type C.

Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.

Having a few LED downlights will not require a Type C.
 

Dave OCD

-
Mentor
Arms
Esteemed
Type B will respond better/quicker to an overcurrent so surely the better option when you don't have to allow for inductive loads or startup current for example.
 
In the days of predominate tungsten lighting I always fitted C 6A on lighting to prevent nuisance tripping from a failing lamp. B or C is mindset providing ADS is provided it is totally irrelevant.
 
N

Nigel

  • Thread Starter Thread Starter
  • #10
In the days of predominate tungsten lighting I always fitted C 6A on lighting to prevent nuisance tripping from a failing lamp. B or C is mindset providing ADS is provided it is totally irrelevant.
Choosing a B or C for me and the sparks I know is down to design.
 

Dave OCD

-
Mentor
Arms
Esteemed
I used to fit C type for the old toroid type wound transformers feeding several halogen downlights with individual outputs, apart from that always B.
 
N

Nigel

  • Thread Starter Thread Starter
  • #12
My whole house is LED with the largest number on one switch six and all on a Type B.
 
D

Deleted member 26818

  • Thread Starter Thread Starter
  • #13
Type B will respond better/quicker to an overcurrent so surely the better option when you don't have to allow for inductive loads or startup current for example.
Both will trip in the same time if the current is enough to cause instantaneous operation.
It’s only the thermal side where a difference would be noted.
 
Ok. Not soley for domestic but you know what I mean.

There is little in a domestic that requires a Type C.

Installing MCBs that trip at 5-10 times the current rather than 2-3 times should not be installed unless required.

Having a few LED downlights will not require a Type C.
I don't actually know what you mean.
 

Andy78

-
Mentor
Arms
Esteemed
I think a lot of it is down to availability too. We buy what the wholesalers have in for domestic stock. The wholesalers will be supplied with the devices that the manufacturers supply for domestic use.
This is generally a range of 6kA B curve breakers. You would have to specifically design for and request a C curve usually.

For instance Hager only do B curve mcbs in their 6kA range, and their reduced height RCBOs (aimed at consumer unit installation) at 6kA are all B curve.
 