raysheehan

Hi all,
Can anyone clarify whether it is O.k to remove a 100mA type s (time delay) Rcd which is upfront of a ammendment 3 splt load 30mA Rcd protected db, and replace it with a isolator? I can't seem to find a reference in the regs book. Any help would be great.
Thanks.
 
  • Optimistic
Reactions: rustynails
why do you want to remove it. it is there to protect the tails both external and internal to the metal CU.
 
Have a shufty, in the yellow OSG page 33.
 
If you use the search function within the forum. There are tons of threads on this subject you can pick information on.
 
  • Agree
Reactions: Rpa07
Its great to have the answe posted to you but you need to search this yourself.

Why do you think the time delay is there?
Many will say yes aslong as you use correct gland ect to ensure the tails dont come in contact with enclosure but i strongly belive it should be kept in place for fault protection on sometimes poor electrode readings.
 
I can hear the sound of hooves...
 
Its great to have the answe posted to you but you need to search this yourself.

Why do you think the time delay is there?
Many will say yes aslong as you use correct gland ect to ensure the tails dont come in contact with enclosure but i strongly belive it should be kept in place for fault protection on sometimes poor electrode readings.

The propriety gland won't prevent accidental contact of the inner single insulated manufactures tails inside a dual RCD CU. Just saying.
 
  • Agree
Reactions: Ian1981
Easy chaps, thought this forum was for asking questions and advice, albeit OP could of not been a bit more conciliatory :)
 
Thought this forum was for discussion and help. I must have come to the wrong place, as for some, it's a chance to beat their Chest and let the rest of the electrical world know they know more! Thanks for your help.
I'm gonna get on my horse and get well away from this site/:-)
 
Hi all,
Can anyone clarify whether it is O.k to remove a 100mA type s (time delay) Rcd which is upfront of a ammendment 3 splt load 30mA Rcd protected db, and replace it with a isolator? I can't seem to find a reference in the regs book. Any help would be great.
Thanks.
Leave it as the time delay will protect the internal manufacturers tail links between rcds and main switch if they short out on the metal enclosure.
 
@raysheehan, sorry that you took the replies wrongly - on the archives, there is every possible answer to most questions.
If you indeed did the search first then I'm sure apologies will come but if you posted the question before any search then it's often said, "we don't do people's homework for them".
Stay on the forum - it's worth it.
 
The propriety gland won't prevent accidental contact of the inner single insulated manufactures tails inside a dual RCD CU. Just saying.

Could be an all rcbo cu ;)
 
Could be an all rcbo cu ;)

OP said 'split load 30mA Rcd protected db', which I take to be dual RCD. But I'm not here to split hairs, unlike some :)
 
  • Agree
Reactions: bigspark17

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Up front 100mA s type Rcd on a TT system.
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Advert

Thread statistics

Created
raysheehan,
Last reply from
7029 dave,
Replies
17
Views
9,102

Advert