succinctly put by ^^^^^ dave. no further comments required, unless they are funny.

showing----.gif
 
  • Funny
Reactions: Pete999
There is nothing wrong with this as the feed in to the garage is fused at 13A already.

2 RCDs in series makes it very hard for you to test the RCD tripping times when you carry out the essential tests before putting your new work in to use.

The additional MCBs won’t make any improvement as the current protection is correct, however they will have no practical negative effect on the installation.

Yes the armour should be earthed at least at one end, preferably the supply end.
No DP isolation is not normally required.
Thanks Dave,
It took a lot of work to get there so thanks for your clear definitive answer.
If others would have done this rather than go off on tangents as to why I wanted more sockets etc we would've been done a lot sooner and I wouldn't have needed to sound like a bolshy git, which I'm not unless people get up my nose.
Again thanks Dave.
 
Thanks Dave,
It took a lot of work to get there so thanks for your clear definitive answer.
If others would have done this rather than go off on tangents as to why I wanted more sockets etc we would've been done a lot sooner and I wouldn't have needed to sound like a bolshy git, which I'm not unless people get up my nose.
Again thanks Dave.

Glad you are now sorted mate.
On the flip side of the coin, if you would have just given the info at the beginning then "we would've been done a lot sooner"
 
Glad you are now sorted mate.
On the flip side of the coin, if you would have just given the info at the beginning then "we would've been done a lot sooner"
Spoon, thanks.
To be fair if you read the original post again, the info is there and the questions are there.
Will have to agree to disagree.
 
succinctly put by ^^^^^ dave. no further comments required, unless they are funny.

View attachment 39825

I dunno, thought my reply was spot on and Spoons weren't bad. Funny enough? :D

Edit; and davesparks came in on the last knockings, just larging it up!
 
Unusual thread that, don't get many garage supply queries.
 
Spoon, thanks.
To be fair if you read the original post again, the info is there and the questions are there.
Will have to agree to disagree.
asking a lot for some forum electricians to read an OP properly before replying. esp. if it's more than 2 lines. :eek::eek::eek::eek::mad:
 
  • Funny
Reactions: Spoon
Spoon, thanks.
To be fair if you read the original post again, the info is there and the questions are there.
Will have to agree to disagree.

That is ok mate... I don't expect everyone to agree with me..
 
  • Like
Reactions: Mr_Freeze
Deleted... Double post..

MODS: Any reason why there isn't a Delete Post option, like the Edit option?
 
asking a lot for some forum electricians to read an OP properly before replying. esp. if it's more than 2 lines. :eek::eek::eek::eek::mad:

and I'm illiterate......
 
Unusual thread that, don't get many garage supply queries.
No only a few every so often, seems that garage installs queries are off the radar:smilingimp::tramcar::raisedhands::tongue:
 
Unusual thread that, don't get many garage supply queries.
No only a few every so often, seems that garage installs queries are off the radar:smilingimp::tramcar::raisedhands::tongue:

Right guys... I've just had a brain wave....
I'm going to start a course where you can become a GI..... No.. not a soldier... but a Garage Installer...
 
  • Like
Reactions: westward10
Right guys... I've just had a brain wave....
I'm going to start a course where you can become a GI..... No.. not a soldier... but a Garage Installer...
Don't Spoon, one of the scams will cotton on and start arranging courses. People will start calling themselves Garage Electricians.
 
Don't Spoon, one of the scams will cotton on and start arranging courses. People will start calling themselves Garage Electricians.

But they will be Garage Electricians..... We love all electricians...
 
  • Like
Reactions: Risteard
Too cold to go outside wiring garages.

Guess what I'm doing tomorrow, pick axe at the ready for me trench.

Got some of this to play on me site radio, fed up with the Vine show;
 
Must say,I just read this thread and the frozen guy comes over as one almighty know it all (bar a bit) :rolleyes: he showed no respect at all for posts that tried to assist
I'm glad I did not post ;) to then have an attempt at assistance shoved down my throat like other members endured
 
I didn't take any offence by any of the OP's posts... Text is a rubbish form of communication as you never know how to take then....
I'm just brill, so I took then all happy... Just imagined him skipping through fields with a flower in his mouth while texting away....
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Upgrading my garage supply.
Prefix
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
103

Thread Tags

Advert

Thread statistics

Created
Mr_Freeze,
Last reply from
Octopus,
Replies
103
Views
13,991

Advert