The earth wire connecting onto the MICC is quite bad. But it's the other end of the earth that worries me. Is it really connected into the neutral terminal block?
Good spot.
It looks like it might be a 2 pole terminal block and it might be that the other (front) set of terminals is used as a MET with the supply TNS braid and the other earth entering from below, and maybe the earth from on top somehow ends up connected to the front set of terminals too. Possibly!
A photo from underneath would be handy.
I certainly agree that pulling the front off that block and seeing what's going on is pretty important!
 
Not double-pole; it looks like a bog-standard retrospective TN-C-S setup with the braid and neutral commoned together in an external block with a green/yellow info label attached, again not ideal but seen it dozens of times. DNO's problem, by all means get them to tidy it up but I wouldn't open it.
 
possibly the supplies are looped door to door.
You were correct this is western powers reply
Good afternoon



The below email has been forwarded to the local team and our engineers have deemed that this doesn’t need a site visit today.



The supply looks safe, it does appear to be looped to next door and as per our new standard techniques once we find a looped supply we have 1 year to re-service this and make sure both properties are fed individually.



I have raised an enquiry for these works and will get our planner to give you a call to arrange a site visit, we will need to gain access to the next door as well so will have to see if we have contact details for them.



If you have any questions in the meantime please don’t hesitate to contact me.



Thanks



Kayleigh Allsopp
Team Support
Lincoln City
Tel: 01522 517623
Team Support: Arren Roe 01522 517626 [email protected]
Team Manager: Dave Naunton 01522 517624 [email protected]
 

Reply to What is this cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Looks very strange to me. Obviously had a new fuse carrier fitted to it at one point but the two cables on the left go to the meter as normal...
Replies
3
Views
680
Evening all, I'm relatively new to the trade and have just moved house. Looking to rewire and was looking at a few things, could someone tell me...
Replies
10
Views
384
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
478
Does anyone know what the cable in the picture is called? Or anything about it? Labelling on the outside is “E SPC Electric Cable 600/1000v” Its...
Replies
9
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock