One final thing to consider for unusually long cables are:
  • If you are failing to meet the Zs for MCB disconnections times, or
  • If you fail to meet 5% voltage drop at the MCB rating (even if it is OK at the fixed load's current that you intended)
They are both a warning signs that you need to consider the design in far more detail.

Basically you might use an RCD to mitigate the high Zs situation, but you also have to consider the risk of a L-N fault also failing to disconnect quickly (as that is not considered a fault by the RCD). So you need to make sure that the over-current aspect (i.e. MCB) will prevent a fire if the cable is overloaded for a long time due to a end-of-line short not resulting in enough current to trip the MCB quickly.
So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cable
 
So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cable
That is the simplest / easiest option to avoid much more analysis. If the cable is already in then looking at a smaller MCB (if available for the distribution board) would be the simplest approach.

If designing from scratch then looking at "6A B-curve" as readily available and usually in the van as a spare would point to using a bigger cable, as here going from 1.5mm to 2.5mm is not a big cost factor.
 
That is the simplest / easiest option to avoid much more analysis. If the cable is already in then looking at a smaller MCB (if available for the distribution board) would be the simplest approach.

If designing from scratch then looking at "6A B-curve" as readily available and usually in the van as a spare would point to using a bigger cable, as here going from 1.5mm to 2.5mm is not a big cost factor.
But what would count as an overly long circuit?
100m? 150m?
 
But what would count as an overly long circuit?
100m? 150m?
One where Zs or VD on the chosen cable CSA, length, and MCB are not being met!

Actual length is immaterial.

Simpler answer is one that is longer than the values giving in the OSG for your situation.
[automerge]1598108407[/automerge]
While an electrician should know how to do all of the calculations, etc, as needed, in practice the whole point of "standard circuits" such as the OSG tables is to avoid the effort and make for a quicker, safer, and cost-effective design process.

You look at the load(s) current requirement, look up a readily available cable/OCPD combination that should be OK for that, and see if your expected length is within the table's values of length & method. If there is nothing else unusual (hot zone, big bundle of cables to need more derating, high inrush currents, manufacturer specific requirements, etc) you don't even need a calculator as it is ready to be fitted!
 
Last edited:
?

So of you was tncs type b 6 amp you are pretty much good up to 90 meter.

But if you was to drop to a 4 amp type b mcb you can go longer but as a rule you know 90 meters will comply at 6 amps

So its best to design a circuit to the breaker size and not your loads...?
 
If it is not in the OSG table you need to go through the full design process really. But for that you also need to know what choices you have for cable and MCBs, etc, that are actually available to you when trying out combinations to see if they meet all of the goals.

MCB/RCBO in particular have to be approved by the DB/CU manufacturer to be sure they are safe (e.g. line up with the busbar, etc) so you need to check the DB make/model and then see what MCB/RCBO/etc are made for it first.
[automerge]1598109948[/automerge]
Many sparks have one or two brands they always use as they know them, have had no problems in the past, can get them are a reasonable price, and usually can get any spares quickly as needed. So they would have a good idea of what they can get for a new design from memory.

If it is an existing design you generally have to work with whatever DB is installed (unless major upgrades are in order) and then you have to do your research.
 
So if its long best bet is to just use a smaller mcb go from 6amp to a 4amp or a c type to a b type or use a bigger cable

No, whatever the length of the circuit you calculate what size cable is required for compliance.
You select the correct size and type of MCB for the circuit and calculate the cable size after that.
 

Reply to Zs and circuit length in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

NICEIC visit the other day… pulled up on length of RM circuit …. Zs 1.30 ohms… RCBO 32amp B type…thoughts on this
Replies
40
Views
3K
Hi all, I was thinking to add some lights like in the attached image, basically twin batten lights to my attic but i'm not familiar with strip...
Replies
4
Views
709
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
791
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock