Pardon my ignorance, but...! Isn't this method merely describing an alternative to 'nulling' the meter with the test leads attached? Or are you saying that the apparent resistance of the (R2) test lead would vary with different installations, depending on the Ze????
It's to do with how the accuracy of the meter becomes more inaccurate, or inconsistent, when the impedances are very low. And as IQ has stated the resulting calculated/measured fault currents vary greatly. By applying a controlled resistance into the circuit, the meter can perform more accurately/consistently.
Reactions: 2 people
If you have a calibration check box could you use one of the resistors there? They are meant to be accurate & consistent and have good connection points
I don't see why not-as long as the connection is sound and safe.
This is the method that we use to ensure a higher accuracy on very low Ze readings.
At first glance, a difference of say 0.09 Ohms does not seem much on a Ze reading but when this value is used (by the instrument or by calculation) to determine PFC then the difference can be massive.
For example: 230/0.10 = 2.3KA 230/0.01 = 23KA
It goes without saying that any connections must be made safely and live testing carried out with equipment in accordance with GS 38.
1 Find a suitable impedance to be used-this should be around about 0.5 Ohms, R2 leads are good for connectivity reasons.
2 Find an outlet on the installation (fused connection unit, socket outlet etc.) that is likely to have a Zs of around 0.20 Ohms.
3 Measure that Zs with the instrument test leads (not the BS 1363 plug lead) and note the value.
4 Measure the Zs again but with the selected impedance (SAFELY) in series with the earth test lead.
5 Subtract the value measured in step 3 from that measured in step 4 and you now have a value for your test impedance (only for that particular installation).
6 Now return to the origin and measure Ze with the test impedance in series with the earth lead.
7 Subtract the value obtained in step 5 and you now have a far more accurate figure for Ze.
Obviously ambient temperature, harmonics, transformer noise etc. all affect readings but unless you have the transformer impedance and the details of the distribution circuit length and CSA etc. then this is about as accurate a reading as you can hope to measure!
Why dont you just test it normally like everybody else I don't understand the logic behind this most readings on TNS supplies are about 0.2 to 0.3 ohms and PME is a little lower, Tower blocks tend to be a lower if you test them in the flat because of the bonding and you don't get access to the main intake but in general it's an easy test why complicate it
The reason
Widdler quote
The outcome
The level of Pfc measured could mean the difference between a rated device passing or failing,with readings that are low he demonstrates the large variation that can occur
I thought it was an excellent and informative post by a guy who definitely knows his onions
Reactions: 2 people
The trouble with this method, at such low readings (instrument resolution of 0.01 Ohm, looking a measurement of 0.0x Ohms), is that it doesn't eliminate the instrument's 'number of digits or counts' error.
So, it's essentially a futile exercise!
The reason
Widdler quote
The outcome
There is only oe approved method of measuring Ze my advice is stick to the industry guidelines in GN3
Yes, but if the DNO's TX is basically in the garden, your MFT Ze/PFC values obtained will be next to useless, so unless you know the TX size and it's impedance along with other details to calculate these values your snookered. Then again, you could always use a very expensive high resolution (0.00X) ELI tester!! IQ's method will give you a higher level of accuracy applying the use of a known/controlled resistance into the circuit being measured....
Oh but i forgot, the picture book GN3 doesn't actually mention anything about thinking outside of the box when needs arise does it!!
I dont see this technique helping.
Lets say the Impedance is 0.02 ohms, at 230 V this equates to 11.5kA.
Now if we introduce an impedance of 0.5 ohms, our circuit is now 0.502 ohms.
At 0.502 ohms standard meters will have a 10% +/- and a 5 digit error +/- around the 0.5 area.
So this equates approx to a +/- of 0.1 ohm, so even with the 0.5 ohm added the reading could be 0.6 ohms or 0.4, a differnace of 0.2 ohm's.
Cheers
Cheers
So without going into another pointless in depth discussion so you can prove a point, when was the last time you applied the +/- 10% and 5 digit error or so, to any value that you measured with you're MFT/EFI tester, and recorded that amended value on a report sheet??
The above method is just a means of enabling a relatively standard MFT/ELI meter to more accurately measure values that are very close to it's ultimate limit, nothing more, nothing less!!
I Dont, but then i wouldnt add a 0.5 ohm impedance to the circuit either, chocolate fireguard!
Well is not going to give you a more accurate result, how can it, when even with the added 0.5 ohm impedance you could get a negative result!
The example i gave was 0.02, now the meter error could be 0.2 ohms, so far from accurate, misleading infact!
Cheers
Cheers
I'm not going to even bother going there....
''Now if we introduce an impedance of 0.5 ohms, our circuit is now 0.502 ohms.''
Hmm is it? 0.5 plus 0.02 is 0.52
sorry old post I know....I personally prefer to use a resistor with value of 1 ohm as its a lot easier to subtract at the end
Cheers[/QUOTE]
Cheers
If you look at the specification of a loop tester such as the megger offerings you'll see that their accuracy is stated as being higher within a certain band of resistances so adding a dummy resistor in can put the test results into the more accurate part of the range.
Cheers
[/QUOTE]
I can't see the point in this method, it's a total waste of time. Just measure ze and move on adding a resistance to the figure only to subtract it will only give you what you would get anyway. If you get 0.02 just record it and recommend suitable mcbs that's all you need to do.
I can't see the point in this method, it's a total waste of time. Just measure ze and move on adding a resistance to the figure only to subtract it will only give you what you would get anyway. If you get 0.02 just record it and recommend suitable mcbs that's all you need to do.[/QUOTE]
The point is to make use of the most accurate part of the test meter's range.
The point is to make use of the most accurate part of the test meter's range.[/QUOTE]
How accurate do we need to be, I'm happy with the approved method described in GN3 which in all fairness is the only method recommended, why complicate this test. My advise is to stick to the approved method because at the end of the day nobody can fault you for complying with your training and non statutory regulations,
This is my final post on this subject, please don't reply as I will not respond.
Thanks David
Higher-accuracy low Ze test procedure
IQ Electrical,
David Marshall,