What else is fed from the same circuit as the lighting? Double check connections and things like a wire or busbar on the wrong side of the clamp termination at the MCB/RCD etc. As already stated check the actual lamp holder where the lamp makes contact for any signs of arcing etc. If the DB is 3-phase try swapping the light circuit to a different phase.
I wouldn't overthink this from a technical point of view, 99% of lamp premature failures are because of something fairly obvious like poor power quality (overvoltage surges and spikes), environmental factors like moisture or vibration and poor terminations or connections etc.
Have you checked that the lamps have actually blown? Poor contact in a lamp holder often manifests itself as perfectly fine lamps appearing to blow.
Reactions: 2 people
I believe the UK mains voltage is a factor,supposed to be 230V but I have seen it above 250V in places.
Supposed by some muppets in offices who haven't got a clue. LV is , and will be for the foreseeable future 250V at the output of the substation transformers
This was our distro the other night just before shutdown
Reactions: 2 people
I have seen 264 that did get the DNO to get arse into gear...
As someone said are the fittings wall mounted or are they posts along the drive. I find eco halogens do not like any kind of vibration. Also you said it was 9 months at least since they were fitted. If the lamps get a lot of switching then they may be coming to the end of their lifespans.
I had a client that had fancy ceiling lights in three rooms. Each fitting had 12 G4s in them. So 36 in total. If each lamp is rated to last a 1000 hrs then when they start to fail it can seem like an endless cycle of changing lamps as knacked ones need replacing. That's partly why some offices etc have all lamps replaced on a relamp regardless of whether they still work.
If all seems OK with the install I would be tempted to put a couple of LEDs in and see if they last better. If they do you can point this out to the client. The UK voltage and European market prob don't help matters either!
I always do Murdoch, this time I got taken in by a cheaper box from screwfix (still not the cheapest though!) with reasonable reviews (I had used it once or twice before and it seemed fine, however with 11 of them it became evident it was poor quality). I have since reviewed the box and also mentioned about it on this forum in a thread I started as I was so disappointed with it.
Still silly though!
Link to the boxes please HHD so we know to avoid them!
HHD, admit you don't know what you're doing.
One of the things I had to study at engineering college was “test methods and reliability.” We used lamps as a case study, all the major suppliers provided samples for endurance and switching tests. The manufacturers can almost guarantee when the lamp will blow when in constant use, IE endurance test. Switched on a regular basis, the time reduced by more than 50%.
Look at the switching.
Sylvania came out as one of the most reliable in endurance.
Reactions: 2 people
Someone else and Tony have mentioned switching, two worst things you can do to an electrical piece of equipment, switch it on, switch it off.
If they're on off on off all day and night they won't last long....
Reactions: 2 people
I think that is a very good suggestion.. thanks!
That sums it up!
You don’t know what you’re doing.
My favorite choice, even the GU10 last for ages.
Yeah...who came up with them bleedin' pir thingies...vital for the lamp producers as much as the users :icon12:
Reactions: 2 people
The thing that annoys me, electricians are basing calculations on a mythical figure. UKPN will never drop the voltage, they can’t afford too. Why can’t the IET accept what is a fact.
I tried lowering the voltage on an 80MVA system using the 33KV OLTC’s, it caused nothing but trouble.
HappyHippyDad
Supporter
Gloucestershire
Lamps blowing!!
HappyHippyDad,
ipf,