I don't buy this. A longer cable won't make 70mA of leakage 'disappear', that's enough to run a 15W lamp. If the leakage from the hood were from L-E then it's going into one of two cores at almost the same potential - the leakage added by the cable's capacitance L-CPC will be hundreds of times more than that removed by the capacitance N-CPC. In any case, when the long and short legs are both connected the RCBO wouldn't trip.
Much more inclined to think it's an N-E fault. Then with the short cable it's much lower resistance and diverts more current. In that case the 70mA is probably quite arbitrary and you will tend to get different numbers with different loads on elsewhere.
Suppose there is a stock fault on the hoods that causes N-E fault on high speed? Have you tested the hood leakage on high speed when isolated from the outside world, e.g. PAT with it sat on the worktop?