16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb

Discuss 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers
 
assuming the cable is 2.5mm (or greater) then a 20A MCB is fine to protect the cable. as it's a dedicated load incapable of overloading the 16A socket, then i can't see a problem.
 
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers

Who has coded it a C2 issue ?
Have they quoted a regulation that it does not comply with ?
 
if the charger is designed to plug into a 16A socket, then the 16A socket is sufficient.

going by the argument of whoever coded it, that means we need to fit 13A socket circuits with a 13A MCB.
 
20 amp should be fine supplying your 16amp socket as you say its covered in OSG part H3.
Out of interest have you hit mainly drains installing your earth rods for your EV chargers ?


I don't know! Scary every time though. Bought a cat scanner for cables but still!! 18th edition takes out the "where reasonably practical" bit. So expect a lot of People hitting utilities
 
16 amp commando and the osg.

cee-red.jpg


Screenshot_20170926-081551.png
 
Because it's an ev charger and like I said in the original post charges for 16 amps constant. Over time I have had them wear the bi metallic strip and start to trip. 20 amps takes the stress off and complies with IET on site guide.

This suggests it is either a poor choice of MCB or actually pulling more than 16A.

A single 16A socket shouldn't need to have an ocpd of more than 16A supplying it, if it does then it is most likely overloaded.
 

Reply to 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top