Three core SWA installed as a new circuit on a TNS supply. Both ends of the SWA are earthed.
Would you/ is it acceptable to include the armour in the R1+R2 calculation (ie in parallel with the core being used as cpc) or should measurement simply be between cores?
Ah... but I know. It's what you think that I also want to know. Do you want it on a plate.
Tell us what you think....and why!
Nope! I know too. It was the very fact that the issue came up on site the other day, I’m keen to see how others respond to the question.
Not meaning to be awkward ( well not a lot anyway!).
if a dog wags it's tail and it's arse at the same time, is it the tail that wags or the arse, or both? or does the tail wag the dog?
Sorry you don’t think I am being real.
Sidestep what?
I think what you should really be asking, is what to do if conduit or trunking is used as a CPC.
Why should I be asking it? No problem, as far as I'm concerned....or the regs.
I'm sure I wouldn't use cable tray as a cpc, though. Unlike an swa, the wiring's not fully contained.
GN8 states (for an SWA with inadequate armour csa to be used as a cpc) that where the armour is earthed and there is also an internal core used as the cpc that the current division between the two parallel conductors cannot be determined and so the separate core should be sized as a stand alone conductor.
Therefore when measuring R1+R2 the armour should not form part of the resistance measurement as the internal core must meet the requirements on its own. Obviously the armour will lower the resistance and presumably assist disconnection but cannot be relied upon.
At last Richard, the answer! :)
In the particular case which prompted the op, the SWA armour, the equivalent csa would have allowed it to be used as the cpc, but with the third core present, not required to.
Reply to A daft question, or not....! in the UK Electrical Forum area at ElectriciansForums.net
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi All, Just looking for some advice: I'm in the process of updating an old cable calc spreadsheet that helps to spit out Zs and Voltage Drop...
If cpc core is present i.e. it's either 5 core three phase or 3 core single phase — is a banjo connected with a brass screw into steel trunking...
Evening all, Having a debate with a colleague about using the SWA armouring and a separate conductor both as CPC's for a circuit. So in theory...