right had an hour to spare

tested from the earth point in the isolator (spot welder end) to armoured sheath and got continuity

other end tested from earth point on the fused supply to the armoured sheath and got continuity

now tested from earth point in the fused supply to the met and got continuity

my question

from the met to the earth point in the isolator (spot welder side) via a fly lead what resistance roughly if any am i looking at
Your looking for a low resistance, if you have a multifunction tester I'd advise you carry out a Zs as well
 
all depends on the csa of the cable or the armour and it's length. figures can be obtained in the osg.

ta will try and find the table
 
Your looking for a low resistance, if you have a multifunction tester I'd advise you carry out a Zs as well

what sub 5 ohns ? and dont have a mft (not a sparky)
 
what are you measuring? a core conductor or armour?
 
what are you measuring? a core conductor or armour?

earth path eg from the isolator by the appliance to the met

as the testers say theres non / not upto standard
 
as i said, the resistance will depend on what you are measuring. what size MCB is feeding the circuit? e.g. if a 32A type B, then i'd expect the resistance to be less than 0.5 ohms.
 
  • Like
Reactions: Corbs
as i said, the resistance will depend on what you are measuring. what size MCB is feeding the circuit? e.g. if a 32A type B, then i'd expect the resistance to be less than 0.5 ohms.

no mcb but 32amp replaceable fuses (i think there type 269)
 
so definitely less than 0.5 ohms, depending on the external Ze could be less. no way to determine without using test meter/s
 
  • Winner
Reactions: Corbs
so definitely less than 0.5 ohms, depending on the external Ze could be less. no way to determine without using test meter/s

thats fine least i have something to go off
 
I can not see any earthing conductors at the mains intake.There is nothing wrong with using the trunking and conduit as the C.P.C. but I can't see how this is earthed back to the consumer unit.
 
  • Like
Reactions: Corbs
I can not see any earthing conductors at the mains intake.There is nothing wrong with using the trunking and conduit as the C.P.C. but I can't see how this is earthed back to the consumer unit.

this is where the stupid sparks came in

they removed a metal board which the conduit was connect to it, and shoved a plastic crappy one in but not redoing / terminating the earth so atm its not earthed as i would of thought they would have done it when they changed the consumer
 
this is where the stupid sparks came in

they removed a metal board which the conduit was connect to it, and shoved a plastic crappy one in but not redoing / terminating the earth so atm its not earthed as i would of thought they would have done it when they changed the consumer
Understand. But AB is saying there should still be a main earth terminal....the original metal board should have been connected to it.
 
Understand. But AB is saying there should still be a main earth terminal....the original metal board should have been connected to it.

yea there is on the side of the main i guess you would call it fuse holder (main incoming supply)

tncs supply if it matters
 
yea there is on the side of the main i guess you would call it fuse holder (main incoming supply)

tncs supply if it matters
Just couldn't see it in the photo and I thought it was the case regarding a metal conduit from the old metal C.U. to the trunking being removed and replaced with flexible PVC conduit removing the earth continuity.
 
  • Like
Reactions: Corbs
Just couldn't see it in the photo and I thought it was the case regarding a metal conduit from the old metal C.U. to the trunking being removed and replaced with flexible PVC conduit removing the earth continuity.

Yep another thing for me to sort / fix
 
Well you would think will give me a bit of ammo anyway
I'd call that a BAZOOKA.......not installing a main earth:mad:
 
No sorry but it was the same connection as the sockets

Coupling and brass bush

Only know this due to the coupling still being on the end of the conduit :D
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
wales
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other

Thread Information

Title
Need Some Advice / Guidance
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
71

Thread Tags

Advert

Thread statistics

Created
Corbs,
Last reply from
Corbs,
Replies
71
Views
7,473

Advert