Zdb
These things are blooming huge!
Oh and £170 :eek:
So the test button is for the RCD and not the AFDD I'm guessing.
Anybody know if there is a prescribed disconnection time that these AFDDs will have to meet?
Just wondering how they can be tested. New setting on the multifunction testers will be next I reckon £££
The all in one 3 module width jobby from MEM Eaton is actually cheaper than the equivalent from Siemens, a 1 module width AFDD that mates with a 2 module width SP+N RCBO.
At the moment there's not many players in the marketplace, hence the ridiculously high pricing. That will change over the next 6-12 months.
There isn’t any way to test AFDDs, without reducing their longevity or making them unserviceable.
All you do is look at the indicator, if it’s green, good to go.
If it’s red, replace.
Its all getting out of hand to be honest. Electricians are being taken for total mugs these days. Glad i dont do any domestic work anymore.
I've never done domestic
Will industrial electricians be exempt from fitting these things, are they only to be fitted in residential properties
I have literally no idea what they are for
I haven't been paying attention to be honest.
These things have been around a while across the pond and it seems there is test equipment available, e.g. Greenlee AFI-100. As has already been suggested, I reckon the MFT manufacturers will waste no time jumping on the bandwagon and launch a new range of 18th ed. testers with this as new functionality.
Fluke T+PRO Electrical Tester 95969327923 | eBay - https://m.ebay.co.uk/itm/Fluke-T-PRO-Electrical-Tester/192561592597?_trkparms=aid%3D111001%26algo%3DREC.SEED%26ao%3D1%26asc%3D52962%26meid%3D8571d8a5e7bf47c19c22ab9f028b3791%26pid%3D100675%26rk%3D1%26rkt%3D15%26sd%3D192561592597%26itm%3D192561592597&_trksid=p2481888.c100675.m4236&_trkparms=pageci%3Aad82fb35-82d4-11e8-9456-74dbd1803e5b%7Cparentrq%3A7af254541640add89ecbb937fff225ca%7Ciid%3A1
Well at least fluke do a tester, so it's another one for the collection.
I just meant that as i work for a big company it doesn't matter to me personally as we fit whatever the spec is for the client.
The price for complying with these new regs is going to be a pain for small domestic jobs when changing boards etc. Just more expense for everyone.
commercial only for them ,you want be putting them in domestic ,it would be the film jaws ,we need a bigger consumer unit or bigger boat .;)
No requirement to install in domestic. Only high risk areas such as flammable sites, places of historic importance and areas with high public usage.
For anyone who’s not seen the regulation covering these AFDD’s it’s as follows;
421.1.7 arc fault detection devices conforming to BS EN 62606 are recommended as a means of providing additional protection against fire caused by arc faults in AC final circuits.
If used, an AFDD shall be placed at the origin of the circuit to be protected.
NOTE: Examples of where such devices can be used include:
•premises with sleeping accommodation
•locations with a risk of fire due to the nature of processed or stored materials, ie B2 locations (e.g barns, woodworking shops, stores of combustible materials)
• locations with combustible construction materials i.e. CA2 locations (e.g. wooden buildings)
• fire propagating structures i.e. CB2 locations
• locations with endangering of irreplaceable goods.
'premises with sleeping accommodation' is a bit ambiguous, though. I'm assuming they mean hotels?
Seems these things are elusive.
Eaton are quoting £160 per combined unit and a 16 day lead time.
They also do not do 3 phase units.
Also according to the NIC presenters, ADDS will not work on a RFC, they didn't give a very good explanation on the film they produced, but the fact that AFDDs won't work on a RFC according to them was something that stuck in my mind.
Perhaps they work by detecting the gaps in the flow of current caused between arcs.
An RFC would have the gaps in current on one conductor filled in by the current flow on the other conductor.
They will work on parallel arc faults on an RFC but won’t detect a series fault on the ring itself although they will detect both types of arc on any equipment connected to the ring or spurs etc as there is no additional leg to compensate.
Whilst AFD's don't detect series arc faults on a ring final cct that mode of fault is not as dangerous on a ring because of the parallel path available for the load current so it's kinda swings and roundabouts....
Things can be in the regs even without a tester - after all there's never been a tester for the magnetic or thermal parts of an MCB/RCBO, only for the residual current part. Dame goes for fuses for that matter. so we have no idea if they still work when doing inspection and testing.
But if a fuse blows or an MCB trips you have test equipment to diagnose the fault quickly and reliably every time.
No such thing with these devices, one might keep tripping due to a natural arc in a circuit (something switching). How do you fault find that.... just start replacing parts at an unnecessary cost.
It is very ambiguous. The Oxford Dictionary says 'Accommodation' is "A room, group of rooms, or building in which someone may live or stay. ‘they were living in temporary accommodation’ "
Doesn't that put every house down as having "sleeping accommodation" ?
Yes, you can just look at the switch or at the melted fuse. But the same applies to the afdd. I thought people meant testing the device itself for correct operation, which you can only do with rcds.
With rcds you can test the rcd itself, and you can ir test the circuit.
With fuses and mcbs you can only test the circuit.
With afdds not sure! Maybe neither?
Yep.
Fortunately 421.1.7 has two softeners for now. It says "If used..." and then gives "Examples of where such devices can be used...". This will change to "shall be used" at some point I guess.
Yep.
But, pinching this from the earlier post, it also has:
If there is a fire and it goes to court and the court says "BS6761 recommend that you use Arc Fault Detection Devices. Why didn't you fit them?" Where would you stand from a legal point of view?
Reply to MCB, RCD & AFDD all in one in the UK Electrical Forum area at ElectriciansForums.net
Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Good morning all, My first post on here! Be kind :) I have had a customer come to me who has a care home for the elderly. I have not carried...
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...