Discuss MCB, RCD & AFDD all in one in the UK Electrical Forum area at ElectriciansForums.net

Whilst AFD's don't detect series arc faults on a ring final cct that mode of fault is not as dangerous on a ring because of the parallel path available for the load current so it's kinda swings and roundabouts....
 
Things can be in the regs even without a tester - after all there's never been a tester for the magnetic or thermal parts of an MCB/RCBO, only for the residual current part. Dame goes for fuses for that matter. so we have no idea if they still work when doing inspection and testing.
 
Things can be in the regs even without a tester - after all there's never been a tester for the magnetic or thermal parts of an MCB/RCBO, only for the residual current part. Dame goes for fuses for that matter. so we have no idea if they still work when doing inspection and testing.

But if a fuse blows or an MCB trips you have test equipment to diagnose the fault quickly and reliably every time.

No such thing with these devices, one might keep tripping due to a natural arc in a circuit (something switching). How do you fault find that.... just start replacing parts at an unnecessary cost.
 
'premises with sleeping accommodation' is a bit ambiguous, though. I'm assuming they mean hotels?

It is very ambiguous. The Oxford Dictionary says 'Accommodation' is "A room, group of rooms, or building in which someone may live or stay. ‘they were living in temporary accommodation’ "

Doesn't that put every house down as having "sleeping accommodation" ?
 
But if a fuse blows or an MCB trips you have test equipment to diagnose the fault quickly and reliably every time.
Yes, you can just look at the switch or at the melted fuse. But the same applies to the afdd. I thought people meant testing the device itself for correct operation, which you can only do with rcds.

With rcds you can test the rcd itself, and you can ir test the circuit.

With fuses and mcbs you can only test the circuit.
With afdds not sure! Maybe neither?
 
It is very ambiguous. The Oxford Dictionary says 'Accommodation' is "A room, group of rooms, or building in which someone may live or stay. ‘they were living in temporary accommodation’ "

Doesn't that put every house down as having "sleeping accommodation" ?
Yep.
Fortunately 421.1.7 has two softeners for now. It says "If used..." and then gives "Examples of where such devices can be used...". This will change to "shall be used" at some point I guess.
 
Yep.
Fortunately 421.1.7 has two softeners for now. It says "If used..." and then gives "Examples of where such devices can be used...". This will change to "shall be used" at some point I guess.

But, pinching this from the earlier post, it also has:
421.1.7 arc fault detection devices conforming to BS EN 62606 are recommended as a means of providing additional protection against fire caused by arc faults in AC final circuits.

If there is a fire and it goes to court and the court says "BS6761 recommend that you use Arc Fault Detection Devices. Why didn't you fit them?" Where would you stand from a legal point of view?
 

Reply to MCB, RCD & AFDD all in one in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Is it possible to put a 16mm swa on a 40a mcb protected by an rcd
Replies
11
Views
801
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
603
Good morning all, My first post on here! Be kind :) I have had a customer come to me who has a care home for the elderly. I have not carried...
Replies
4
Views
3K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
883

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock