Discuss Earth fly lead size & requirement in the UK Electrical Forum area at ElectriciansForums.net
Gringoking88
Hi all,
Hope you are all well and all is good!
I am installing a sub board being fed by a 80A SP+N Metal Switch Fuse at source, this is feeding a 25mm 3 core SWA at a length of about 2 meters to the main DB (both boards are metal). I am being challenged in saying that I have to add an earth fly lead at both ends, preferably the same size as the CPC e.g. 25mm, as the glands will be fine for continuity of CPC into the armour.
Am I being super safe or just a moron, whats the right answer?
Thanks all.
i would add fly leads to ensure that the steel armour is reliably earthed. seen a couple of sites where the continuity from earth bar to metal casing is poor. if you do the adiabatic, bearing in mind the restivity of the armour, 10mm should suffice.
Are you really competent to carry out this work, if so you would be looking at what your earthing arrangement is to the existing installation.
Thanks Telectric, my thoughts exactly, but was just going to be over kill with the fly lead.
Because you are in the DIY section and messing with the DNO switch fuse? and digging around inside the existing CU therefore dangerous and maybe notifiable?
Are you talking about leads from the glands' banjo (or better still Earthing nut / Piranha nut) to the related earth terminals?
Yes, you should do it as you can't always be sure the box will be in great contact, not corrode a bit with time, or even (probably not here) be able to cope with the fault currents.
  • Simple answer is to go with the CSA from Table 54.7 in the regs, which in your case is 16mm.
  • Or you can go with the adiabatic calculation, and the fastest way to check that would be Table B4 from the OSG which should no change in Zs 0f 0.4 ohms from from 10mm to 16mm, implying 10mm is fully OK for a 80A fuse and 5s disconnection times.
  • Also you also really should consider the limits of Table 54.8 for the TN-C-S case in case there is extraneous stuff bonded to the CU earths, which typically means a 10mm minimum.
TL;DR Use 10mm or 16mm as you have lying around in this case!
Just looked over again and realised you have a CPC in the 3 cores of the SWA, that takes away the issue of TN-C-S bonding as you already have the sizeable end-end path.
However, you should still be designing to cope with an internal cable fault/penetration incident even if very unlikely, and so you should have the armour ends rated for fault-clearing of the 80A fuse.
You could get away with just 10mm at the only feed end, but I would say it is still good practice to have both ends able to cope with any fault currents. In reality 6mm at both ends should be sufficient, but 10mm would be meeting all requirements without assumptions of current sharing, etc.
Reply to Earth fly lead size & requirement in the UK Electrical Forum area at ElectriciansForums.net
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
Hello everyone, Following on from my previous post where I received advice on taking a spur off a 40a feed (thank you). I performed the work...
Hi, I have always used banjos when earthing the armour on an SWA but have now switched to earthing nuts. I am making off a 10mm fly lead to the...
Hi all. Could I ask some advice please regarding SWA banjo fly lead sizing. Can anyone explain what sizing or how you size the required earth...
4K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
4K