JLH520

I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use multiple electric heaters on a 32amp breaker if needed. The circuit consists 4 double sockets plus one single socket on the end, in a weatherproofed box on the wall outside. As it happens, I rarely need to use electric heaters in there, as there are plumbed radiators too, so the radial is easily over specced and currently has only a 16amp breaker.

Now I need to add two extra double sockets outside to power two 2500 watt infra red heaters under a gazebo (each has a 13 amp 3 pin UK plug fitted, they won’t be hardwired). I am hoping to be able to add these sockets by running a spur from the conservatory radial circuit as it could comfortably cope with the draw from the heaters. My intention was to continue a 4mm twin and earth spur to these additional two sockets outside so that the whole radial is safely capable of handling 32 amps.

The problem is that a fused connection unit which handles a fuse above 13 amp doesn’t seem to exist, so I’m wondering how best to safely connect this spur to my radial circuit and isolate the outside circuits if need be?

Any helpful suggestions on how to implement this would be greatly appreciated
 
Last edited:
  • Like
Reactions: pc1966 and DPG
A 45A double pole switch would be suitable if you want a means of isolating the external part of the circuit.
 
A 45A double pole switch would be suitable if you want a means of isolating the external part of the circuit.
Ok, thanks for the suggestion. I am aware that typically, taking a spur off a radial when there is more than one additional socket to be added, a 13 amp fused connection unit should be used - then you can add as many sockets as you like on that spur (within reason, and please correct me if I am wrong here!).
I suspected this would be the same when using 4mm T&E (on both the original radial and the new spur), capable of carrying more amps, only this would need a higher rated fuse (up to 32amps?)
Is it acceptable within the regs to add just a double pole switch at the end of the indoor section of the radial so that I can isolate all the outside sockets beyond it? Not sure if regs also require some sort of additional fused unit before going outside with a further 3 sockets (1 existing, plus 2 new additional sockets).
Thanks.
 
Ok, thanks for the suggestion. I am aware that typically, taking a spur off a radial when there is more than one additional socket to be added, a 13 amp fused connection unit should be used - then you can add as many sockets as you like on that spur (within reason, and please correct me if I am wrong here!).
I suspected this would be the same when using 4mm T&E (on both the original radial and the new spur), capable of carrying more amps, only this would need a higher rated fuse (up to 32amps?)
Is it acceptable within the regs to add just a double pole switch at the end of the indoor section of the radial so that I can isolate all the outside sockets beyond it? Not sure if regs also require some sort of additional fused unit before going outside with a further 3 sockets (1 existing, plus 2 new additional sockets).
Thanks.
let me correct you first. no disrespect, but, 1. it's not pedantically a spur. a spur is only off a ring circuit. off a radial it's a branch.
2. as rthe MCB (up to 32A for a 4mm radial) will protect additional branches (in 4mm) from overload, a FCU is not required.

so just tap in where convenient. add a branch for the new sockets, uprate the MCB accordingl to the load )32A if clipped direct and not subject to derating due to insulation). happy days. ??
 
Ok, thanks for the suggestion. I am aware that typically, taking a spur off a radial when there is more than one additional socket to be added, a 13 amp fused connection unit should be used - then you can add as many sockets as you like on that spur (within reason, and please correct me if I am wrong here!).
I suspected this would be the same when using 4mm T&E (on both the original radial and the new spur), capable of carrying more amps, only this would need a higher rated fuse (up to 32amps?)
Is it acceptable within the regs to add just a double pole switch at the end of the indoor section of the radial so that I can isolate all the outside sockets beyond it? Not sure if regs also require some sort of additional fused unit before going outside with a further 3 sockets (1 existing, plus 2 new additional sockets).
Thanks.
Surely if your continuing the circuit from the last socket it wouldn't be classed as a spur youd just be extending the radial circuit?
 
Ok, thanks for the suggestion. I am aware that typically, taking a spur off a radial when there is more than one additional socket to be added, a 13 amp fused connection unit should be used - then you can add as many sockets as you like on that spur (within reason, and please correct me if I am wrong here!).
I suspected this would be the same when using 4mm T&E (on both the original radial and the new spur), capable of carrying more amps, only this would need a higher rated fuse (up to 32amps?)
Is it acceptable within the regs to add just a double pole switch at the end of the indoor section of the radial so that I can isolate all the outside sockets beyond it? Not sure if regs also require some sort of additional fused unit before going outside with a further 3 sockets (1 existing, plus 2 new additional sockets).
Thanks.
U can't spur off a radial... its just a case of extending the radial circuit. Would you consider it a 'spur'if you went from the last socket on the circuit? You're thinking of the rules for adding additional outlets from a ring final circuit arrangement.
 
What Telectrix said! ?

................ .................. ........... Five wordd
 
  • Like
Reactions: pc1966
I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use multiple electric heaters on a 32amp breaker if needed. The circuit consists 4 double sockets plus one single socket on the end, in a weatherproofed box on the wall outside. As it happens, I rarely need to use electric heaters in there, as there are plumbed radiators too, so the radial is easily over specced and currently has only a 16amp breaker.

Now I need to add two extra double sockets outside to power two 2500 watt infra red heaters under a gazebo (each has a 13 amp 3 pin UK plug fitted, they won’t be hardwired). I am hoping to be able to add these sockets by running a spur from the conservatory radial circuit as it could comfortably cope with the draw from the heaters. My intention was to continue a 4mm twin and earth spur to these additional two sockets outside so that the whole radial is safely capable of handling 32 amps.

The problem is that a fused connection unit which handles a fuse above 13 amp doesn’t seem to exist, so I’m wondering how best to safely connect this spur to my radial circuit and isolate the outside circuits if need be?

Any helpful suggestions on how to implement this would be greatly appreciated
IT is a
I have a dedicated radial from the consumer unit to my conservatory. This was installed using 4mm twin and earth as it gives the option to use multiple electric heaters on a 32amp breaker if needed. The circuit consists 4 double sockets plus one single socket on the end, in a weatherproofed box on the wall outside. As it happens, I rarely need to use electric heaters in there, as there are plumbed radiators too, so the radial is easily over specced and currently has only a 16amp breaker.

Now I need to add two extra double sockets outside to power two 2500 watt infra red heaters under a gazebo (each has a 13 amp 3 pin UK plug fitted, they won’t be hardwired). I am hoping to be able to add these sockets by running a spur from the conservatory radial circuit as it could comfortably cope with the draw from the heaters. My intention was to continue a 4mm twin and earth spur to these additional two sockets outside so that the whole radial is safely capable of handling 32 amps.

The problem is that a fused connection unit which handles a fuse above 13 amp doesn’t seem to exist, so I’m wondering how best to safely connect this spur to my radial circuit and isolate the outside circuits if need be?

Any helpful suggestions on how to implement this would be greatly appreciated
There is a recommendation that loads of 2Kw and above need to be on their own dedicated circuit, not fed via a 13 A spur
 
  • Like
Reactions: superspark
never agreed with thatpete. it may have been relevant when a house had only 1 RFC (ncluding kitchen) but these days it's rare to see a non-kitchen RFC loaded to >5A or 6A. we had a 2.2kW hot tub , 2.2kW sauna, 3 freezers, washer, fumble dryer, all on a 16A radial (garage). cable used to get slightly warm. made ito a RFC (when sauna was added) to a 32A RFC just to be safe.
 
  • Like
Reactions: Sapper
There is a recommendation that loads of 2Kw and above need to be on their own dedicated circuit, not fed via a 13 A spur
I think we've established that this wont be on a 13A spur... its on a radial, wired in 4mm, which could have a 32A OCPD if someone changes it back from a 16.

As above, if you want to isolate the outside sockets, then a 45A double pole switch ... (for a cooker or shower - no fuse) before going outside will suffice.


Edit, Afterthought: If youre doing any work to this circuit, you must ensure it is RCD protected... i dont think it was mentioned on the OP
 
Last edited:
There is no reason why it cannot be extended in 4.0 and upgraded to 32A however as previously mentioned the installation method may not permit it. If you are going to contain this cable in conduit then 32A is not an option.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
spot on.
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
How is the new cable going to be installed.
 
  • Like
Reactions: Jim_e_Jib
How is the new cable going to be installed.
…was planning to run 4mm SWA to the new sockets. Had planned to use a short run (approx 1 metre) of 4mm twin and earth in a conduit between the two sockets rather than use SWA between the two sockets. Is 4mm T&E permissible in conduit over this short distance?
 
…was planning to run 4mm SWA to the new sockets. Had planned to use a short run (approx 1 metre) of 4mm twin and earth in a conduit between the two sockets rather than use SWA between the two sockets. Is 4mm T&E permissible in conduit over this short distance?
Contained in conduit it would not be rated at 32A unless it is singles.
 
  • Like
Reactions: Jim_e_Jib
If the bit in the conduit only feeds one socket, then it doesn't need overload protection - just short circuit protection.
 
never agreed with thatpete. it may have been relevant when a house had only 1 RFC (ncluding kitchen) but these days it's rare to see a non-kitchen RFC loaded to >5A or 6A. we had a 2.2kW hot tub , 2.2kW sauna, 3 freezers, washer, fumble dryer, all on a 16A radial (garage). cable used to get slightly warm. made ito a RFC (when sauna was added) to a 32A RFC just to be safe.
Firstly why is a guy who is 80 still working? secondly Tel nice to see you are still alive ?
 
I'm not being funny here but why would anyone in their right mind want to use a considerable amount of electricity to warm outside ? The world is in a bad enough state already ?? No offence intended.
 
I'm not being funny here but why would anyone in their right mind want to use a considerable amount of electricity to warm outside ? The world is in a bad enough state already ?? No offence intended.

Indeed. 5 kilowatts of electricity to heat the outdoors!
 
What are you drying Brian, a marquee ? ?
 
Laundry from holiday cottages. American sized washing machine and tumble drier.
even though, eack kWH will dry to a set level. 5kW will just be quicker then a 3 kW unit. energy in = energy out, and all that.
 
Firstly why is a guy who is 80 still working? secondly Tel nice to see you are still alive ?
am only taking on small, non-mauling jobs now. legs are knackered and lungs are dicey. be 75 in a week. another few years before son needs to find somewhere for my tools. he's already scrounged the 1553 i bought off you 7 years ago. crikey, time flies when you're a coffin dodger.
 
75?

You’ll be looking forward to a life of diddy little diy jobs, watching YouTube videos of tractors, engines and other machinery just moving…. Not actually doing anything and drinking copious amounts of coffee…

That’s what my 75 year old dad does
 
75?

You’ll be looking forward to a life of diddy little diy jobs, watching YouTube videos of tractors, engines and other machinery just moving…. Not actually doing anything and drinking copious amounts of coffee…

That’s what my 75 year old dad does

Sounds OK to me that! Swap coffee for beer though.
 
  • Like
Reactions: Dave OCD
am only taking on small, non-mauling jobs now. legs are knackered and lungs are dicey. be 75 in a week.
There's more life in you, you old dog, you could take a job in stacking sleeves at big orange House and showing us young ones it can be done.
 
even though, eack kWH will dry to a set level. 5kW will just be quicker then a 3 kW unit. energy in = energy out, and all that.
MUCH quicker than a UK domestic drier. It uses moisture sensors and 'fuzzy logic' to keep the electricity consumption to a minimum for a non heat pump drier, but I still see £ signs in front of my eyes when I watch that meter light flashing.
 
That little red light can be a handy tool when you repair a heater or immersion heater for example. Just compare the flash rate between off and on and you know straight away that it's drawing current and ok - or not. ?
 
I had to laugh at this thread, and most threads because by the time they are towards the end they bear no resemblance to the initial subject😁
 
Thank you all for (A) putting me straight on a couple of points, and (B) providing the answers I was looking for.

To clarify a couple of points - yes the circuit is, and will continue to be RCD protected and I will extend onto the end of the radial, rather than cutting in between the existing sockets (not sure if that would change anything.)

I will also change the circuit MCB to a 32 amp to cope with the heaters.

Thanks again.
And then you will use a multifunction tester and do a r1 r2 test, a Zs test, a RCD trip time test and complete a Minor works cert,,,,Wont you
 
And the band played believe it if you like as my gran used to say. 😄
 
  • Funny
Reactions: Jim_e_Jib
And then you will use a multifunction tester and do a r1 r2 test, a Zs test, a RCD trip time test and complete a Minor works cert,,,,Wont you
Not forgetting insulation resistance as well.
 
  • Like
Reactions: Markyd
IT is a

There is a recommendation that loads of 2Kw and above need to be on their own dedicated circuit, not fed via a 13 A spur
Normally hard wired, yes, but it says heater has a 13 amp plug top, Which is man fact fitted, i dont agree that a 2.5 or 3kw heater especially outside should be on a plug top, as we all know , seperate supply For these they could be on for hours.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email