Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin and eath cable and what looks like a Cat5 cable. The twin and earth is currently in connector blocks. This cable runs from the junction box straight to my Hager fuse board and is on a 32amp breaker. It is listed at the box as Car Charger which i imagine is done in case we want to add a car charger in the future. I want to remove the junction box and add an outdoor IP66 double socket but ideally would like to use the exisiting cable (6mm twin and earth) and the exisiting breaker (32amp) is this safely possible as i know both are higher than required. From what i have seen outdoor double sockets are normally wired in 2.5mm twin and earth and have an 13amp breaker?
 
It would be advised to get a spark in to down grade the fuse to a 16 amp in the Cu board and give you a minor test cert,
He can use the 6mm cable with out down grading that.
 
It's fine to do as they suggest as long as there is 30ma RCD protection.
 
  • Like
  • Agree
Reactions: DefyG and DPG
It would be advised to get a spark in to down grade the fuse to a 16 amp in the Cu board and give you a minor test cert,
He can use the 6mm cable with out down grading that.
There's no benefit to downrating the circuit protection if there's a 6mm^2 cable there. That said, I'm not a fan of an EVSE being connected to a 32A protective device rather than a 40A as otherwise it's running at the full rating of the protective device for potentially many hours at a time.
 
I would imagine it’s a 32A type A RCBO.
But agree, 40A would be better.

Is this 32A in the main consumer unit, or in a sub board on its own?
 
I assume this isn't going to be used for an EV charger.
 
  • Like
Reactions: Spoon
The OP is only fitting a double socket to it.. It's not going to be pulling more than 32A
 
The OP is only fitting a double socket to it.. It's not going to be pulling more than 32A
Granted. My comment relates to how it was installed for the intended use. As such I don't believe that 32A was the correct choice. It is, however, ideal for a socket circuit.
 
  • Like
Reactions: leesrubberroom
I assume this isn't going to be used for an EV charger.
No not at the moment anyway, i am just looking to put the outside socket in for December period to plug xmas lights into then after that i will remove and put back original junction box
 
I would imagine it’s a 32A type A RCBO.
But agree, 40A would be better.

Is this 32A in the main consumer unit, or in a sub board on its own?
It is in the main consumer unit
 
It is in the main consumer unit
Ok... Its not a problem, but as others have mentioned, A 32A breaker would be running at its limit while charging....

You're not using the circuit for car charging, so not really a valid point.


A double socket, although possible to plug in 2 x 13A loads, may only be rated for 20A, so I would advise having the breaker size reduced to 16A, just to protect the socket. (Will never reach that value if only xmas lights)
 
A double socket, although possible to plug in 2 x 13A loads, may only be rated for 20A, so I would advise having the breaker size reduced to 16A, just to protect the socket. (Will never reach that value if only xmas lights)

Ok, I don't want to come across like some sort of grumpy old fart.. (which I am) and maybe I need to listed to Marie Carry sing "All I want for christmas is you" 20 more times, while headbutting a wall but....
I know where you are coming from, for safety reasons, but as most sockets are wired back to 32A breakers I don't really see the need and expense in changing the breaker.
 
if you were designing a circuit from scratch, knowing it was just going to be one outside socket (or two, being a double) then you wouldnt put it on a 32A.
Youde be protecting the cable.... which isnt an issue here, as its oversized anyway... ah... wait a minute......



Ok, scratch that. Im now thinking along the lines of an originally designed 32A radial wired in 4mm with regular double sockets on it. You could have the same 26A load plugged into any of them.

Ok. Just leave the 32A in place. Its not an issue.

"Grumpy old fart"?..... No, i think that particular scouser is laid up at the moment :)
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wellingborough
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Can i wire an outside socket to a junction box located for a car charger?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
Jordanntfc,
Last reply from
littlespark,
Replies
14
Views
2,362

Advert