Actually managed to kill 2 PIRs in succession yesterday. The first I got SL and N mixed up (who uses the black core of a 3C+E as neutral? honestly), which killed it dead, tripping the breaker in the process. Schoolboy error.

The second, well I don't feel it's 100% my fault.

The PIR I had been asked to change had stuck permanently in the on position, and the client had turned off the breaker until it was replaced. It was controlling 2 twin 6ft fluorescent tubes in a garage, so 280W of fluoro lighting. I replaced it with an Eterna PIR, which instructions state good for 300W of fluorescent lighting.

However, on re-energising, I had the same problem - the new PIR was stuck on permanently. You could hear a faint click 'on' when it sensed motion, and again click 'off' after the time delay, but the SL terminal remained live. I noted that the starter for one of the twin fluoros had gone, so the tubes were flickering indefinitely as they attempted to light up.

What I guess happened is the constant start up current due to the failed fluoro starter caused the contacts in the PIR to weld closed. Can anyone confirm that this is likely to be the case, or if they have come across a similar problem before?
 
Just seems like bad luck all round on the day there
 
Oooops. You lean by your mastakes.
 
Yeah, I guess so. I can't help feeling that starter failure on fluorescents is inevitable, and if it is that that killed the PIR, it should at least be warned against in the instructions.
 
The PIR is rated for 300W inductive load (fluor), does that include surge on start or just continuous loading? And if you are running 280W load off it anyway you are pretty close to the full rating. Personally, I would have looked for something with a higher rating just for peace of mind.
 
I think the welding bit may be correct on the PIR. It is definitely a problem with contactors of all kinds the inrush currents. Most manufacuturers give inrush current data. But notionally I think you are in the range of 10x to even 100 times inrush current. Even at the lowest estimate that's enough to nuke the delicate contacts in a PIR. Of course that would be times 2, maybe use a suppressor?
non-compensated ferromagnetic ballast - 10-15 x In for 5-10ms
compensated ferromagnetic ballast - 20-60 x In for 0.5-1ms
electronic ballast 30-100 x In for 0.5ms
 
Last edited:
  • Like
Reactions: Pretty Mouth
The PIR is rated for 300W inductive load (fluor), does that include surge on start or just continuous loading? And if you are running 280W load off it anyway you are pretty close to the full rating. Personally, I would have looked for something with a higher rating just for peace of mind.
It just says max 300W for fluorescent load, no more info than that
 
I'd be the same , I'd be wary of maxxing out the fluorescent rating on the pir

Wouldn't trust it
 
I think the welding bit may be correct on the PIR. It is definitely a problem with contactors of all kinds the inrush currents. Most manufacuturers give inrush current data. But notionally I think you are in the range of 10x to even 100 times inrush current. Even at the lowest estimate that's enough to nuke the delicate contacts in a PIR. Of course that would be times 2, maybe use a suppressor?
non-compensated ferromagnetic ballast - 10-15 x In for 5-10ms
compensated ferromagnetic ballast - 20-60 x In for 0.5-1ms
electronic ballast 30-100 x In for 0.5ms
Thanks @Vortigern . I've not had to use a suppressor before, what sort of thing should I use?

Do you think that the fluorescent starter being defective would have worsened the problem (I assume the problem was the starter, as both tubes of the pair were failing to light up properly).

I have suggested changing to LED, although the max load for that is even lower, 200W max 8 lights.
 
@Pretty Mouth just google inrush suppressor. I imagine you are going to get a cycling of the inrush as the starter was not working but I am not sure that would make matters worse as the circuit does not finally excite.
 
  • Like
Reactions: Pretty Mouth
@Pretty Mouth just google inrush suppressor. I imagine you are going to get a cycling of the inrush as the starter was not working but I am not sure that would make matters worse as the circuit does not finally excite.
Thanks for this @Vortigern . I had a read up on NTC thermistors, and while I now get the idea of them, I wouldn't know how to select one for this purpose, or what considerations there are for installation. For a low value job such as this, I'm not going to pursue it any further - they can have a manual switch instead! Cheers
 
  • Like
Reactions: Deleted account

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Killed a PIR, fluorescent lighting
Prefix
N/A
Forum
Lighting Forum
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Vortigern,
Replies
12
Views
2,476

Advert