In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm
Why TT, just run a 1.5mm^2 swa including the armour as CPC and bonding and it meets the regs.
Cheapest option