brman
I'm trying to get my head around using the adiabatic to calculate minimum size earth conductors and realised I am getting myself confused over which fuses they relate to and how they relate to the tables in the OSG.
This is a theoretical situation, I am just trying to make sure I understand things properly.....
So..... (TN-S system)
1) Main earth conductor => supplier fuse.
So a BS88-2 @ 80A needs 400A for 5s => sqrt(400^2 * 5) / 115 = 7.7 so min csa = 10mm2?
Or should I use k = 143 (table 54.2) and get 6.25, ok still 10mm2.....
2) Main earth bonding => supplier fuse again so same as above.
So how come the OSG (table 4.4, P40) says this depends on the line/neutral conductors? They aren't included in the sums above.
And how come those tables require a larger main earth compared to the earth bonding? What am I missing?
Thinking further, if I have a max Ze of 0.8 my PEFC is only 290A so my BS88 fuse will take more like 20s to go. Should I be worrying about that?
Hmmm... thinking further. if I use my PEFC in the adiabatic I get sqrt(290^2 * 20) / 115 = 11.3, so CSA = 16mm2. Is this what I should actually be using?
Sounds sensible to use the PEFC but it still doesn't explain why the tables relate things to the live conductor size and the tables don't define the supplier fuse type which affects things.
So, I am confused :dizzy2:
This is a theoretical situation, I am just trying to make sure I understand things properly.....
So..... (TN-S system)
1) Main earth conductor => supplier fuse.
So a BS88-2 @ 80A needs 400A for 5s => sqrt(400^2 * 5) / 115 = 7.7 so min csa = 10mm2?
Or should I use k = 143 (table 54.2) and get 6.25, ok still 10mm2.....
2) Main earth bonding => supplier fuse again so same as above.
So how come the OSG (table 4.4, P40) says this depends on the line/neutral conductors? They aren't included in the sums above.
And how come those tables require a larger main earth compared to the earth bonding? What am I missing?
Thinking further, if I have a max Ze of 0.8 my PEFC is only 290A so my BS88 fuse will take more like 20s to go. Should I be worrying about that?
Hmmm... thinking further. if I use my PEFC in the adiabatic I get sqrt(290^2 * 20) / 115 = 11.3, so CSA = 16mm2. Is this what I should actually be using?
Sounds sensible to use the PEFC but it still doesn't explain why the tables relate things to the live conductor size and the tables don't define the supplier fuse type which affects things.
So, I am confused :dizzy2: