Umarhafiz

We had our bathroom renovated about 10 years ago and the original builder had left the shower wire too short and i didnt bother to get it fixed right away as we had another shower in the new loft extension done by the same builder around the same time. A few years go by and i then decided to ask someone to have a look and suprisingly no one had a simple answer i dont know if the electricians in my area are no good or it genuinely is a difficult or risky thing to do. to this day i have not found anyone who wants to do it so i have come here to get a better idea of what i could do or what is the best option. The bathroom has been tiled and there is a bath tub under where the shower is meant to be. Sorry if ive not given enough information im not very clued up when it comes to bathroom wiring or any wiring really.
 
I think we need some more information here - what type of cable, where is it and how short is short?!

Some pics might help if you can post some.
 
  • Like
Reactions: DPG
The best option is to replace the cable for a longer one from the shower isolator to the shower. This would possible mean removing tiles to get to the shower. But as the cable is too short to reach the shower now then it looks like tiles will have to be removed anyhow.
Is the shower fitted now?
What size shower?
What is on the other side of the wall where the shower is (or to be fitted)
 
The best option is to replace the cable for a longer one from the shower isolator to the shower. This would possible mean removing tiles to get to the shower. But as the cable is too short to reach the shower now then it looks like tiles will have to be removed anyhow.
Is the shower fitted now?
What size shower?
What is on the other side of the wall where the shower is (or to be fitted)
There is of course the possibility that the existing cable wasn't clipped inside it's short run inside a stud wall - in which case with a huge amount of luck and patience you can sometimes use the old one as a draw to pull in a new one.
 
  • Like
Reactions: Spoon
I think we need some more information here - what type of cable, where is it and how short is short?!

Some pics might help if you can post some.
Will get some pics as soon as possible im not at home at the moment. Sorry.
 
The best option is to replace the cable for a longer one from the shower isolator to the shower. This would possible mean removing tiles to get to the shower. But as the cable is too short to reach the shower now then it looks like tiles will have to be removed anyhow.
Is the shower fitted now?
What size shower?
What is on the other side of the wall where the shower is (or to be fitted)
Shower has not been fitted and behind where the shower is meant to go is the outside of the house.
 
Shower has not been fitted and behind where the shower is meant to go is the outside of the house.

As @Rockingit has mentioned, is it a solid wall?
Has an isolator been fitted?
What size cable?
 
one way or another it can be sorted, but a site visit would be needed to ascertain the best way without dynamite excessive disruption. i could manage that, but it's right on the edge of my travelling distance.
 
IMG_20210514_145755.jpg
IMG_20210514_145802.jpg
IMG_20210514_145815.jpg
IMG_20210514_145843.jpg
 
looks to be an easy job to be honest! Chisel out some more of the block around the cable for access, three crimp n shrinks and job done.
 
you would need 6.0mm insulated crimps (yellow ones). but they would need to be securely crimped as they will be carrying c. 40A, so must be as tight as a duck's arse. (I'm assuming 6mm cable from your pics ).
 
you would need 6.0mm insulated crimps (yellow ones). but they would need to be securely crimped as they will be carrying c. 40A, so must be as tight as a duck's arse. (I'm assuming 6mm cable from your pics ).
Ok thanks for the info
 
The “shrink” part of crimp n shrink is heat shrink sleeving.

it goes around the crimped cables, and when heated will shrink and pull tight against cable and crimps, just for added safety. Much more robust than insulating tape.

it is a simple job for someone with the right tools. As mentioned, you could have 40A running through it, and you don’t want to be in the shower when that joint suddenly fails.
 
freeze his goolies off when it goes cold.
 
  • Funny
Reactions: dodger421 and Spoon
The “shrink” part of crimp n shrink is heat shrink sleeving.

it goes around the crimped cables, and when heated will shrink and pull tight against cable and crimps, just for added safety. Much more robust than insulating tape.

it is a simple job for someone with the right tools. As mentioned, you could have 40A running through it, and you don’t want to be in the shower when that joint suddenly fails.
Ok that makes sense thank you
 
You would also need to put some decent heatshrink around all the joints and both cables.
 
Yes.... and they don’t come insulated, so definitely heat shrink over them

SEPARATELY
 
  • Like
Reactions: pc1966
You also need to consider if It might actually be cheaper to get someone in to do it as you'd need:
-a short section of 10mm T+E (and probably have to buy more than you want)
-2 x 10mm crimps
-1 x insulated 4mm crimp
Heat shrinking in various sizes
6mm earth sleeving
+ Crimping tool if you don't have one

It all adds up!
 
This is probably pushing DIY limits, as you will need the proper crimp tool and some means of heating the heat-shrink. An electric paint stripper gun can be used for that with great care as they can also melt PVC insulation and destroy it.
 
You also need to consider if It might actually be cheaper to get someone in to do it as you'd need:
-a short section of 10mm T+E (and probably have to buy more than you want)
-2 x 10mm crimps
-1 x insulated 4mm crimp
Heat shrinking in various sizes
6mm earth sleeving
+ Crimping tool if you don't have one

It all adds up!
Yh i was thinking that as i also wouldnt know if ive crimped it properly and stuff like that anyone know how much i should be paying for a job like this?
 
If you have space to put it in, and it is definitely away from any water, but you have some means of accessing it for any maintenance, then something like this junction box is a better bet:

If it were me and I could somehow get the cable in the roof space above it, then using something like that and a longer run of new wire down to the shower would be easier.
 
  • Like
Reactions: loz2754
Would it be an idea to fit the shower unit higher?
It might be simpler extending the water pipe up, than the cable down.
 
Yh i was thinking that as i also wouldnt know if ive crimped it properly and stuff like that anyone know how much i should be paying for a job like this?
You will get a variety of opinions on this!
Mine is that if you can find someone very local who doesn't charge more for 1st hour because it's local, it's less than an hours work to just extend the cable. £45 -£70 bracket.
Would it be an idea to fit the shower unit higher?
It might be simpler extending the water pipe up, than the cable down.
I wondered that earlier too. A John Guest coupler and away you go...
 
Would it be an idea to fit the shower unit higher?
It might be simpler extending the water pipe up, than the cable down.
Great idea how have i not thought of that already. So i would just need to make a chanel in the tile for the cable and just extend the water pipe instead which is much safer i assume.
 
You’ll just need to chisel away enough brick away to get a push fit coupler over the pipe.
Don’t let any chips of brick enter the end of the pipe.
 
Is left hand section designed for rear entry, and could you actually move it down?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
I need help with an electric shower wire which is too short
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
70

Advert

Thread statistics

Created
Umarhafiz,
Last reply from
telectrix,
Replies
70
Views
11,781

Advert