Spudnik
Hi chaps,
Just been to look at a kitchen which needs a few bits doing ie couple of new circuits etc.
Looking at the origin, TNS, and it appears to have 16mm tails with 10mm M.E. feeding a 60A MEM BS88 (i think) switchfuse, when then feeds to the 16th editionCU a few meters away in 16mm T&E.
Now, would you insist on the sub-main being replaced due to the main earth being undersized?
Have to say im not too sure.
Comments appreciated.
Ta