Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.
 
Aico 3000
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Andy78

Andy78

-
Mentor
Esteemed
Arms
Earthing conductor and bonding arrangements immediately ring some alarm bells ....
 
haptism

haptism

-
  • Thread Starter Thread Starter
  • #3
Earthing conductor and bonding arrangements immediately ring some alarm bells ....
There is acceptable Ze, main earth at the board is single g/y 16mm, water and gas bonded with 10mm also.
 
Andy78

Andy78

-
Mentor
Esteemed
Arms
There is acceptable Ze, main earth at the board is single g/y 16mm, water and gas bonded with 10mm also.
Next thing I would worry about is did the cable run need RCD protection due to the nature of the install ?

The service fuse carrier is always marked 100A as the max rating of fuse. The fuse would need to be checked to ascertain if the tails need fusing down after it.
 
D

Deleted member 26818

Measure the PFC and then conduct the Adiabatic equation, to determine whether the conductors are under sized.
 
DPG

DPG

-
Esteemed
Arms
Patron
What is the FCU supposed to switch off in the garage?
 
D

Deleted member 26818

Probably just wired up the FCU incorrectly.
Most likely find the FCU is now switching the ring rather than the socket.
 
haptism

haptism

-
  • Thread Starter Thread Starter
  • #9
Measure the PFC and then conduct the Adiabatic equation, to determine whether the conductors are under sized.
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
 
L

luka B

-
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
I had one last week where Main fuse blew twice in a week .. was replaced by electric co. I thought maybe the cause was too much usage ... Took the Main Fuse ( no seal ) ... but alas it was a grey fuse with no writing on it !! so i was none the wiser .
 
Strima

Strima

-
Esteemed
Arms
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.
 
haptism

haptism

-
  • Thread Starter Thread Starter
  • #12
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.
Yes I will be doing that, lesson learnt today, check service head before any works done, not afterwards.
 