Did a job earlier in a new build, part of a 5 year old new build estate in the darkest depths of kent. Anyhow opened up CU and saw 16mm tails so assumed would be on 80a fuse as there not huge demand. Then outside to check service head and main fuse is labelled 100a ?, the tails are 16mm t&e.
I did nor remove the fuse carrier to check the actual fuse as it was sealed :rolleyes:

Anyhow my point is, ive already installed new circuit and have to issue an EIC, I will be writing in comments box write what I found and that it looks wrong. However looking forward what should I do about this. The customer wont be happy me turning off all the power; I told him to contact the people he bought the house from and raise the point.

Another thing I found includes a spur that don't switch off the load in garage that its labelled to do. Its not right is it, brand new house as well, and theres hundreds of them.
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

Andy78

-
Mentor
Arms
Esteemed
Earthing conductor and bonding arrangements immediately ring some alarm bells ....
 

Andy78

-
Mentor
Arms
Esteemed
There is acceptable Ze, main earth at the board is single g/y 16mm, water and gas bonded with 10mm also.
Next thing I would worry about is did the cable run need RCD protection due to the nature of the install ?

The service fuse carrier is always marked 100A as the max rating of fuse. The fuse would need to be checked to ascertain if the tails need fusing down after it.
 
D

Deleted member 26818

Measure the PFC and then conduct the Adiabatic equation, to determine whether the conductors are under sized.
 

DPG

-
Arms
Esteemed
Advent Win
What is the FCU supposed to switch off in the garage?
 
D

Deleted member 26818

Probably just wired up the FCU incorrectly.
Most likely find the FCU is now switching the ring rather than the socket.
 
  • Thread Starter Thread Starter
  • #9
Measure the PFC and then conduct the Adiabatic equation, to determine whether the conductors are under sized.
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
 
Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
I had one last week where Main fuse blew twice in a week .. was replaced by electric co. I thought maybe the cause was too much usage ... Took the Main Fuse ( no seal ) ... but alas it was a grey fuse with no writing on it !! so i was none the wiser .
 

Strima

-
Arms
Esteemed
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.
 
  • Thread Starter Thread Starter
  • #12
Note on the cert stating you're unable to verify the size of the DNO fuse.

Not your place to start pulling fuses. You may contact the DNO to find out but they probably don't know either.
Yes I will be doing that, lesson learnt today, check service head before any works done, not afterwards.
 
  • Thread Starter Thread Starter
  • #13
Next thing I would worry about is did the cable run need RCD protection due to the nature of the install ?

The service fuse carrier is always marked 100A as the max rating of fuse. The fuse would need to be checked to ascertain if the tails need fusing down after it.
Theres definitely no rcd protecting the tails; my issue is I cannot see if the t&e is mechanically protected or not when it goes into building so will note this on the cert also. Is it usual to run tails in t&e on new builds and put in conduit ?? That's a really subjective question.

Second thoughts its a lash up, t&e comes out switch fuse (also stating 100A) through a bush and ring, theres no gland; hangs in the air with no fixings then goes into the wall. Lash up if you ask me
 
T

Toneyz

Looks like a separate 16mm main earth is run alongside the t&e, I cannot see if the t&e is mechanically protected on way to cu but I doubt it, so yeh, no rcd for that added to the list. I will need to take fuse out of carrier and have a look, maybe its 80A afterall. Yeh PFC looks good, don't have results to hand.
Is this T&E that goes to the C.U. a sub main?
 
  • Thread Starter Thread Starter
  • #15
Is this T&E that goes to the C.U. a sub main?
Im not entirely sure as all wiring is back entry into CU, proper tails go from main DNO Fuse to meter and then to switch fuse; from the switch fuse its t&e. So I assume yes it goes to CU
 