Can someone remind me
Is a type 2 breaker = to a type B
Can't find my file
Many Thanks
 
No, the maximum fault loop values are lower for old 3871 type 2's than newer 60898 B's.
 
Lenny
That would possibly explain the problem- are the starting characteristics similar eg Type B, 3 times, C, 7to 10 times
Been to look at an old control panel. 3 of the type 2 rated 25amp breakers were defective (very unusual!)
Been informed a "sparky" was holding then in whilst starting the motors.
My line of attack- obtain Flc of motors- check cables and sizes- and rate and size breakers for type C (motor rated with infrequent starts- if many starts type D)
 
A type D breaker should not be fitted with a motor, only fit a type C. The overloadand contactor fitted on the motor should only do 6 starts an hour, if more starts are reqired fit an inverter. more expensive but its the right way
 
A type D breaker should not be fitted with a motor, only fit a type C. The overloadand contactor fitted on the motor should only do 6 starts an hour, if more starts are reqired fit an inverter. more expensive but its the right way


Agreed.
 
Why do Merlin Gerin and every other manufacturer give a table in their catalogues for motor starters
showing the recommended MCB IN TYPE H, TYPE C & TYPE D
eg
4kW 5.5HP 3 phase c 20amp d 16amp
Are you saying the manufacturers are wrong or do you have a reason. Is it to do with the let through energy, in that case you have to size the contactors to suit.Or
Is it the type of co-ordination (where things are allowed to be damaged to a certain degree ) under a fault condion.
The parts then have to be replaced
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 pole minature circuit breakers
Prefix
N/A
Forum
Electrician Talk | All Countries
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
controlman,
Last reply from
controlman,
Replies
5
Views
1,522

Advert