Jay

Hi All,

Can anyone help me out with a problem I have.

I have to install 2 extra 3ph industrial sockets on a circuit which already has 2 existing on it.

The 3ph MCB protecting the existing 2 is rated at 32A so could it hold an additional 2.

The circuit will be protecting / supplying 4 industrial heaters rated at 9kW - is this too much for a 32A MCB.

The main sw. fuse is rated for 125A which supplies 6 single phase MCB's (1x20A, 3x16A, 1X10A, 1x6A) aswell as the 400V socket circuit.

Thank You.
 
Im trying to find out suitable MCB Rating for the additional two 3ph sockets.

The formula that I'm using to calculate the current is - Watts / √3 Line Voltage × cos Power Factor Angle

which gives me 18000/√3 x 400V × 0.95 (guesstimate!!!) = 27A therefore a 32A would suffice but i'm worried about the main sw. fuse

blowing with too much loaded on it.

What do you think?

Thank you for replying
 
With heaters there was no need to include PF so it will drop a bit more.

As for the main supply:
The first question is will all the heaters be on at any one time, IE thermostats, etc. If yes you can apply diversity.
(Not that you need to)
 
Im trying to find out suitable MCB Rating for the additional two 3ph sockets.

The formula that I'm using to calculate the current is - Watts / √3 Line Voltage × cos Power Factor Angle

which gives me 18000/√3 x 400V × 0.95 (guesstimate!!!) = 27A therefore a 32A would suffice but i'm worried about the main sw. fuse

blowing with too much loaded on it.

What do you think?

Thank you for replying

That's a bit different to asking if 4 X 9KW on a 32A breaker is suitable, ...isn't it?? lol!! So now it's just 2 heaters!!
 
sorry i knew i phrased that wrong just as i sent it.

No there will be 4 heaters in total on the board but i just need to accomodate the extra 2.

Thats why I am asking if you think the Main Sw. Fuse will hold the additional 2.
 
Well as the Main Switch is rated at 125A, i don't think you'll have much of a problem there. you haven't exactly got that much else on that DB have you..
 
The main sw. fuse is rated for 125A which supplies 6 single phase MCB's (1x20A, 3x16A, 1X10A, 1x6A) aswell as the 400V socket circuit(32A).

I just dont want to install it and then have to increase cable / mcbs down the line .

What do you think?
 
Tony I dont understand what youre trying to say.

I thought diversity only counts if you dont have everyhting running at the same time.

In my case all circuits will be running continuosly.
 
ah ok now i understand.

Do you think I should install an extra circuit though or should I redesign the incoming supply?
 
The main sw. fuse is rated for 125A which supplies 6 single phase MCB's (1x20A, 3x16A, 1X10A, 1x6A) aswell as the 400V socket circuit(32A).

I just dont want to install it and then have to increase cable / mcbs down the line .

What do you think?

This is a 3 phase DB, so you have in effect 3 X 125A!! Are you still worried?? ...lol!!
 

Reply to 3PH MCB's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
310
Does a SPD need a dedicated way? I need an extra way in this unit for a 3 phase car charger As you can see its a small unit with no extra...
Replies
43
Views
1K
So here is the thing Rhere is an old MEMSHIELD TPN+E Board that is pretty mich obsolete. The only place that sells their breakers would be Ebay...
Replies
5
Views
884
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
20
Views
601
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
968

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock